Good question.
The arrangement meets the definition of "main earthing system" in ESRs; so yes installing it is high-risk PEW and so requires inspection.
Search found 966 matches
- Mon Jan 13, 2025 10:44 am
- Forum: Generators and Solar
- Topic: Plug in generator installation connection point
- Replies: 7
- Views: 1626
- Thu Jan 09, 2025 11:57 am
- Forum: Generators and Solar
- Topic: Plug in generator installation connection point
- Replies: 7
- Views: 1626
Re: Plug in generator installation connection point
Yes 2.5(g) sets a default of only supplying installation (or part) from genset via MSB; but immediately allows an Exception provided 2 conditions are met. As published (using "and"), both conditions must be met - making it completely pointless. Was supposed to be "or" - but no-one (including me) spo...
- Wed Jan 08, 2025 10:18 am
- Forum: Generators and Solar
- Topic: Plug in generator installation connection point
- Replies: 7
- Views: 1626
Re: Plug in generator installation connection point
It's still switching supply to load supplied from that DB between 2 sources; one being "normal supply" and the other being an "alternative supply". Physical location of the source selection device makes no difference to how the requirements apply, but will affect the detail of how you comply with th...
- Tue Jan 07, 2025 10:40 am
- Forum: Generators and Solar
- Topic: Plug in generator installation connection point
- Replies: 7
- Views: 1626
Re: Plug in generator installation connection point
There is no rule prohibiting connection of an alternative supply at a DB, to supply all / part of that DB's load. It is well-established practice for large installations with a centralised alternative supply to distribute that supply via (essential power" submains to those DBs that supply essential ...
- Tue Dec 24, 2024 7:18 am
- Forum: Damp Situations
- Topic: Louvred Pergola in zone 1 of spa
- Replies: 3
- Views: 2279
Re: Louvred Pergola in zone 1 of spa
Given the dimensions, I reckon this thing is specifically intended for use with a spa pool- and is being sold as such. There's nothing else most peaople would want to fit roof & lights over, and louvres around. But likely not designed specifically around our NZ Zones. Or European Zones, which ours a...
- Sat Dec 21, 2024 7:05 am
- Forum: Damp Situations
- Topic: Louvred Pergola in zone 1 of spa
- Replies: 3
- Views: 2279
Re: Louvred Pergola in zone 1 of spa
I agree the lights and the lead of this unit are in Z 1. So you should not install them. However the Wiring Rules apply only to the electrical installation; not to appliances plugged into it. What people do later is up them, and all we can do is advise. It's acceptable to install a GPO outside Z1 if...
- Fri Dec 20, 2024 10:29 am
- Forum: Switchboards
- Topic: PEC Submain from Non M.E.N switchBoard
- Replies: 3
- Views: 3609
Re: PEC Submain from Non M.E.N switchBoard
Item (v) arises only if taking option (B) of item (iv). Option B is that supply to the outbuilding DB is via one or more other DB that are in other outbuildings, and not direct from MSB. Noting that there is no valid option of supply via DBs in main building, only via DBs in other outbuildings. Keep...
- Tue Dec 17, 2024 12:43 pm
- Forum: Generators and Solar
- Topic: Removing and replacing PV panels
- Replies: 3
- Views: 2270
Re: Removing and replacing PV panels
Whether it should be classed as low risk PEW is a very different question from whether it is classed as low risk PEW.
Exactly the same as for a mains entry box.
Exactly the same as for a mains entry box.
- Mon Dec 16, 2024 2:07 pm
- Forum: Generators and Solar
- Topic: Removing and replacing PV panels
- Replies: 3
- Views: 2270
Re: Removing and replacing PV panels
On my opinion it's maintenance / repair / replacement;
not installation work/
No different from replacing a fitting.
Or a length of mains cable; which is also high risk when installing, but low risk when maintaining
not installation work/
No different from replacing a fitting.
Or a length of mains cable; which is also high risk when installing, but low risk when maintaining
- Fri Dec 13, 2024 3:26 pm
- Forum: Appliances
- Topic: Is a Hob (Cooking Appliance) "enclosed"?
- Replies: 1
- Views: 1583
Re: Is a Hob (Cooking Appliance) "enclosed"?
Why "2000" edition? this clause was never mandatory. The wording "open cooking surface" was added in A3, (2003), including examples of what is intended to be covered, as well as the not explaining examples not included. "open cooking surface" refers to the user's access to the hot bits. It's not abo...
- Fri Dec 13, 2024 3:17 pm
- Forum: Standards and Legislation
- Topic: Non-Electrical Workers
- Replies: 4
- Views: 2566
Re: Non-Electrical Workers
basically all electrical equipment is either a fitting or a collection / assembly of fittings. The 3 main types of such assemblies are "works" , "electrical installations", "appliances". All defined in Act as mutually exclusive. Demarcation between works & installation is 'point of supply"; generall...
- Thu Dec 12, 2024 5:20 pm
- Forum: Standards and Legislation
- Topic: Non-Electrical Workers
- Replies: 4
- Views: 2566
Re: Non-Electrical Workers
4836 does not deal on electrical worker vs non-electrical worker. It deals with managing the risks of work - whether that's electrical work or anything else - either in or near LV /ELV installations & equipment. And while it deals in competence generally; it doesn't get into specific qualifications ...
- Fri Nov 29, 2024 3:18 pm
- Forum: Switchboards
- Topic: PEC Submain from Non M.E.N switchBoard
- Replies: 3
- Views: 3609
Re: PEC Submain from Non M.E.N switchBoard
Short answer: this config is non-compliant If installing PEN submain i.a.w. 5.5.3.1 (b), item (iv) says the submain can come either(A) from MSB, or (B) via intermediate DB(s) . If using (B), then (v) kicks in, and integrity of the PEN must not depend on any connections to terminals in the intermedia...
- Fri Nov 29, 2024 12:45 pm
- Forum: Generators and Solar
- Topic: Domestic or non domestic solar
- Replies: 1
- Views: 1875
Re: Domestic or non domestic solar
The key is in the definitions in "3000": 1.4.52 Electrical installation 1.4.53 ditto domestic 1.4.54 ditto multiple 1.5.55 ditto residential ICPs are a management tool, but they do not in any way define whether this is one installation or two. Nor does the metering arrangement. Assuming it's correct...
- Fri Nov 29, 2024 12:33 pm
- Forum: Electric Vehicles and Charging Systems
- Topic: RCD protection of mode 3 charger
- Replies: 5
- Views: 5556
Re: RCD protection of mode 3 charger
1 Yes, an "MEN switchboard as defined in ESR 4 must be connected to an earth electrode. 2 3000 doers not permit more than 1 MEN swbd within same installation; except for an outbuilding. so correct can have a freestanding pedestal (as outbuilding), but not a "EV swbd" mounted in / on same building as...
- Thu Nov 28, 2024 11:49 am
- Forum: Electric Vehicles and Charging Systems
- Topic: RCD protection of mode 3 charger
- Replies: 5
- Views: 5556
Re: RCD protection of mode 3 charger
A freestanding pedestal type structure would conform to definition of "outbuilding". And in a non-residential installation, - the Guideline requirement to take supply from an MEN swbd would apply; but - the Clause 7.9 prohibition on supply from an outbuilding would not apply. So if arranged with PEN...
- Wed Nov 27, 2024 12:31 pm
- Forum: Electric Vehicles and Charging Systems
- Topic: RCD protection of mode 3 charger
- Replies: 5
- Views: 5556
Re: RCD protection of mode 3 charger
I suspect I am the source of the answer being quoted here Perfectly possible to have an EV charging station that includes a switchboard. And yes there could be good afr doing so, especially in a commercial environment. In that context; we need to look at what the applicable documents has to say abou...
- Wed Nov 20, 2024 4:49 pm
- Forum: Forum User Guidelines
- Topic: getting registered
- Replies: 1
- Views: 3914
getting registered
Have had someone ask how to get registered onto the Forum.
And couldn't answer, unless it lies behind the "login" system?
And couldn't answer, unless it lies behind the "login" system?
- Fri Oct 18, 2024 8:21 am
- Forum: Inspection
- Topic: Main Switchboard Location - High Risk Mains Work?
- Replies: 2
- Views: 5694
Re: Main Switchboard Location - High Risk Mains Work?
Pete is correct; it's not "mains work" so not something we can properly use s reason to issue "fail" RoI ie one that states the high-risk PEW we inspected has not been done "i.a.w the regulations and / or will not be electrically safe when connected. Remembering that it's not a case of refusing to i...
- Thu Oct 17, 2024 10:53 am
- Forum: Inspection
- Topic: on property hv lines
- Replies: 2
- Views: 3827
Re: on property hv lines
You are looking in the right place. Within the def for "installation" there are two options; installations with point of supply and installations without. This example is in the "with PoS" part. Meaning that the installations starts at the PoS... so off to that definition Which depends -, in part, b...
- Wed Oct 16, 2024 1:24 pm
- Forum: Standards and Legislation
- Topic: ESR 25 (d) vs AS/NZS3000:2007 7.8.2.1
- Replies: 3
- Views: 12191
Re: ESR 25 (d) vs AS/NZS3000:2007 7.8.2.1
True the fact that ESR 75 applies to the owner of the installation, so for construction wiring, that will be the builder; the PAs often just don't get done.
So errors / faults don't get picked up by the assessor
So errors / faults don't get picked up by the assessor
- Sun Oct 13, 2024 10:27 pm
- Forum: Generators and Solar
- Topic: ASNZS 5033 Ground mount Solar fencing
- Replies: 2
- Views: 4648
Re: ASNZS 5033 Ground mount Solar fencing
Why would it comply with 2021 edition?
ESRs cite 2012 edition +A1 +A2 ; with one further change in the citation.
Nothing to prohibit following a later edition, provided it complies with cited edition.
ESRs cite 2012 edition +A1 +A2 ; with one further change in the citation.
Nothing to prohibit following a later edition, provided it complies with cited edition.
- Wed Oct 09, 2024 9:09 am
- Forum: Distribution, Networks & Metering
- Topic: 63MW solar farm legislative requirements
- Replies: 2
- Views: 6028
Re: 63MW solar farm legislative requirements
1 Correct such an assembly of fittings is "works", "not an electrical installation" Both terms being defined in Electricity Act, and are mutually exclusive. There is some apparent (but not legal) crossover; as installations can include generation; and generating stations typically include consuming ...
- Mon Sep 16, 2024 9:47 am
- Forum: Standards and Legislation
- Topic: Clauses that need to be amended or clarified
- Replies: 1
- Views: 4115
Re: Clauses that need to be amended or clarified
I don't think so.
There's a considerable difference in risk between a wall limiting a Zone, and a ceiling limiting a Zone.
Water seldom falls upwards, and splash seldom reaches the ceiling
(even when the ceiling is low enough to replace the default height measurement as limit of Zone).
There's a considerable difference in risk between a wall limiting a Zone, and a ceiling limiting a Zone.
Water seldom falls upwards, and splash seldom reaches the ceiling
(even when the ceiling is low enough to replace the default height measurement as limit of Zone).
- Tue Sep 10, 2024 1:47 pm
- Forum: Transportable Installations
- Topic: Transportable Tiny Home Stand alone Installation
- Replies: 1
- Views: 5308
Re: Transportable Tiny Home Stand alone Installation
Correct that if there is no provision for external supply, it's not a "connectable installation". So not required to comply with "3001" by ESR 60(1). Can comply, but not required to. Correct that 4509.1 requires an earth electrode - even if the only real function of it is to avoid the unit being blo...
- Mon Sep 09, 2024 10:28 am
- Forum: Earthing and Bonding
- Topic: Earth stake directly into concrete
- Replies: 5
- Views: 25182
Re: Earth stake directly into concrete
Agree with Doug on pretty much all his points. But to me the question isn't really about effectiveness of the electrode; it's more compliance with the requirement. Which is "effective contact with moist soil" - and that is always going to be a subjective rather than an objective assessment. Looking ...
- Sat Aug 17, 2024 9:39 am
- Forum: Testing & Verification
- Topic: COC Test Results
- Replies: 4
- Views: 16526
Re: COC Test Results
Agree it doesn't happen often that anyone bothers to arrange an independent, temporary, supply for testing.. Most times it's easier to wait, and do these tests after initial connection to (grid) supply). Technically that would count as "connection-for-testing"; and - provided all test results are sa...
- Fri Aug 16, 2024 11:11 am
- Forum: Testing & Verification
- Topic: COC Test Results
- Replies: 4
- Views: 16526
Re: COC Test Results
There is NO requirement for any test results to be included on a CoC. The regulatory requirement is that testing - as per "3000" must be done (by someone) prior to connection. Note here's also NO requirement that the person who did PEW must do the testing. Nor issue the CoC. These things must be don...
- Mon Aug 12, 2024 9:51 am
- Forum: Earthing and Bonding
- Topic: Earth stake directly into concrete
- Replies: 5
- Views: 25182
Re: Earth stake directly into concrete
In my opinion concrete cannot be considered a covering that maintains moist soil . Concrete may be slightly porous, but not very. Note it's used to make water tanks, also boats. True they put in additives to make it even less porous for those jobs. For sunken basements they paint it with special pai...
- Wed Aug 07, 2024 6:33 am
- Forum: Off Topic/General Electrical Discussions
- Topic: Emergency Lighting Insalation Standard - Diagram Query
- Replies: 2
- Views: 14064
Re: Emergency Lighting Insalation Standard - Diagram Query
Agree they are n/c contacts. But (being pedantic) when test button is pressed, they will not be opening, but closing (else the E-lights would be switched 'off" instead of "on") The convention for schematic drawings is that "normal" means de-energised; rather than whatever state may be perceived as n...
- Mon Jul 22, 2024 10:41 am
- Forum: Standards and Legislation
- Topic: Shuttered socket outlets
- Replies: 3
- Views: 15952
Re: Shuttered socket outlets
There is currently no requirement for "3112" sockets to have shutters. I believe there are specifications that must be met IF shutters are provided. It's not an NZ vs Oz thing; it's a safety-conscious vs cheapest product thing. There was a move some time ago to try to mandate use of shutters (or equ...
- Tue Jul 09, 2024 10:53 am
- Forum: Standards and Legislation
- Topic: Does "works" require Certification
- Replies: 1
- Views: 9780
Re: Does "works" require Certification
Certification (& inspection)is only required for general / high-risk PEW "on an installation".
ESCs a bit different; also needed for connection to supply done at supply fuse.
Check the wording in the relevant ESRs
ESCs a bit different; also needed for connection to supply done at supply fuse.
Check the wording in the relevant ESRs
- Sat Jul 06, 2024 8:42 am
- Forum: Inspection
- Topic: Fault loop Impedance and PSCC Inspection requirement or not?
- Replies: 2
- Views: 13371
Re: Fault loop Impedance and PSCC Inspection requirement or not?
Inspection is required for mains work done on an installation by an installer. Provision of short circuit protection and fault protection for mains is not part of that, because ESR 32 makes it the responsibility of the lines company. Accordingly, these are not matters we need to look at when inspect...
- Sat Jul 06, 2024 8:25 am
- Forum: Inspection
- Topic: Replacing a PV Inverter
- Replies: 3
- Views: 13813
Re: Replacing a PV Inverter
Not sure what would result from a different inverter being found if audited.
But should not reflect back on you.
I suspect few others wool be recording this info on their RoI.
If anything, the fact that you've re4corded this (non-required?) info would tend to confirm that a swap had been done.
But should not reflect back on you.
I suspect few others wool be recording this info on their RoI.
If anything, the fact that you've re4corded this (non-required?) info would tend to confirm that a swap had been done.
- Thu Jul 04, 2024 9:36 am
- Forum: Inspection
- Topic: Replacing a PV Inverter
- Replies: 3
- Views: 13813
Re: Replacing a PV Inverter
Under ESR 6A (1) replacement of fittings is low-risk PEW.
So no CoV required.
And therefore cannot be high-risk PEW, so no inspection required either.
So no CoV required.
And therefore cannot be high-risk PEW, so no inspection required either.
- Fri Jun 28, 2024 11:50 am
- Forum: Transportable Installations
- Topic: Inverter in connectable installation
- Replies: 16
- Views: 61182
Re: Inverter in connectable installation
Remember 2022 edition has not yet been cited by ESRs. Until that changes, 1.5 is compliant with 16 A overcurrent protection. Note also that even when this clause does come into force, it will only apply to the installation of the wiring; not to issuing a WoEF for an existing unit. Assuming the citat...
- Thu Jun 27, 2024 8:30 am
- Forum: Transportable Installations
- Topic: Inverter in connectable installation
- Replies: 16
- Views: 61182
Re: Inverter in connectable installation
Correct that RCD protection is required for all final subcircuits. The usual, and accepted, way to use an isolated-output inverter as alt supply for a caravan (or part of one) is to fed it into ma change-over switch (make B4 break, 460V rated). Correct that circuits on separated supplies must have p...
- Thu Jun 27, 2024 8:08 am
- Forum: Standards and Legislation
- Topic: New Registration Endorsements
- Replies: 5
- Views: 19624
Re: New Registration Endorsements
Yes, you are correct; both PV (at LV) and MPG are high risk. I should have known. And should have checked. Why they have picked the MPG and not the PV for this set of changes is unknown. Even stranger is that they have decided to distinguish between PEW in a cardiac-protected area and other medical ...
- Wed Jun 26, 2024 9:33 am
- Forum: Standards and Legislation
- Topic: New Registration Endorsements
- Replies: 5
- Views: 19624
Re: New Registration Endorsements
The thing about a "PV installation" is that in most cases it not just a PV installation. PV by itself is not classified as high-risk PEW. You can do whatever on the array; and it's either not PEW (for ELV) or general PEW (for LV arrays). The part that's high-risk is the mains-parallel inverter. Note...
- Tue Jun 25, 2024 9:49 am
- Forum: Selection and Installation of Wiring Systems
- Topic: Conduit vs Flexible conduit
- Replies: 3
- Views: 17681
Re: Conduit vs Flexible conduit
Some people think that orange"high impact" conduit is HD.
It's not.
It's classified as MD, albeit having more impact resistance than the grey version.
It is intended for u/g use; and has less UV resistance than the grey.
When used above ground & exposed to sunlight, it breaks down and becomes brittle.
It's not.
It's classified as MD, albeit having more impact resistance than the grey version.
It is intended for u/g use; and has less UV resistance than the grey.
When used above ground & exposed to sunlight, it breaks down and becomes brittle.
- Sun Jun 23, 2024 8:23 pm
- Forum: Standards and Legislation
- Topic: New Registration Endorsements
- Replies: 5
- Views: 19624
Re: New Registration Endorsements
1 Why did they choose Mains Parallel Generation? Because it's classified as high-risk PEW in ESR 6A. whereas PV is not. 2 if you miss out on the Grand-parenting of an Endorsement, what other avenues are there to gain these Endorsements so far, nothing. And not likely to be anytime soon, because EWRB...
- Fri Jun 21, 2024 8:02 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: Conduit vs Flexible conduit
- Replies: 3
- Views: 17681
Re: Conduit vs Flexible conduit
"Heavy duty" and 'flexible" are two completely different aspects
some conduit is HD.
some conduit is flexible.
Some is both.
And some is neither
some conduit is HD.
some conduit is flexible.
Some is both.
And some is neither
- Sun Jun 09, 2024 10:37 am
- Forum: Standards and Legislation
- Topic: Imported Electrical Installations
- Replies: 4
- Views: 18293
Re: Imported Electrical Installations
There are a number of errors and omissions, some minor and others more serious. The methodology described in this Guide depends on an "Installation SDoC", which appears to be mandatory. However there appears to be n Regulation or Gazette notice to provide the mandate. And while the guidance correctl...
- Fri Jun 07, 2024 6:00 am
- Forum: Standards and Legislation
- Topic: Imported Electrical Installations
- Replies: 4
- Views: 18293
Re: Imported Electrical Installations
Thanks for posting that.
I knew there was something coming on this.
I knew there was something coming on this.
- Thu Jun 06, 2024 9:44 pm
- Forum: Standards and Legislation
- Topic: PEW and appliances/ Fittings
- Replies: 3
- Views: 15342
Re: PEW and appliances/ Fittings
remember SDoCs are only needed IF the item is a DMRA. I don't believe this would fit in any DMRA category. DMRAs are generally household type items. can spend a lot of time in the rabbit-hole of finding relevant product Standards. Probably wasted time. bottom line is: if it's done right, no-one gets...
- Thu Jun 06, 2024 2:38 pm
- Forum: Standards and Legislation
- Topic: PEW and appliances/ Fittings
- Replies: 3
- Views: 15342
Re: PEW and appliances/ Fittings
1 assembly of fittings Correct that this newly-assembled plug-in equipment is not part of an installation. Installation is defined in the Act; it starts at "point of supply", and excludes any appliances (regardless of whether plugged in or directly connected) Most - but not all assemblies of fitting...
- Sat Jun 01, 2024 9:14 am
- Forum: Electric Vehicles and Charging Systems
- Topic: GEN 2 Tesla EV Charger
- Replies: 1
- Views: 12767
Re: GEN 2 Tesla EV Charger
It's not about what the charger manufacturer calls for; it's about what Worksafe and NZ Standards call for So - regardless of what the charger manufacturer may say (apparently , for Tesla,different things at different times) ; you should be following Clause 7.9 of "3000" (2018 edition) and the Works...
- Fri May 03, 2024 12:08 pm
- Forum: Standards and Legislation
- Topic: ESC and Council Building Inspectors
- Replies: 6
- Views: 26503
Re: ESC and Council Building Inspectors
1st 2 copies of any CoC, RoI, or ESC go to a) the person whom asked for work to be done; and b) the person who issued the cert (who has to keep a copy for 7 years). A number of other 'entities' are entitled to request a copy; including the TLA. They have to make their request to the issuer. For a Co...
- Thu May 02, 2024 2:42 pm
- Forum: Standards and Legislation
- Topic: ESC and Council Building Inspectors
- Replies: 6
- Views: 26503
Re: ESC and Council Building Inspectors
You are not wrong. and (surprise surprise!) EWRB is. As is the meter provider. It's not possible to limit an ESC; it automatically applies to everything that gets connected by the action of connecting. If this is the company i think it is; they have a long history of trying to minimise their liabili...
- Thu May 02, 2024 2:37 pm
- Forum: Standards and Legislation
- Topic: Main Switch Height - BTS
- Replies: 5
- Views: 22869
Re: Main Switch Height - BTS
it may be non-compliant 9with a non-mandatory Standard); but there's no way it can be called unsafe.
In fact ESR 25 says that as long as it complies with the cited version it is electrically safe!
Clearly Worksafe has at least one idiot in it's employ.
In fact ESR 25 says that as long as it complies with the cited version it is electrically safe!
Clearly Worksafe has at least one idiot in it's employ.