Search found 25 matches
- Tue Oct 17, 2023 9:01 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: N pin on socket used for other means
- Replies: 3
- Views: 20733
Re: N pin on socket used for other means
I have a site that has motors controlled via VFD. The motors are run in suitable VFD cable. The client wants the motors to connect via plug and socket arrangement. Rather than a 3+E socket they want to use a 3+N+E but want to use the N pin to continue the screen through. I don't like this at all, I...
- Tue Oct 17, 2023 8:36 pm
- Forum: Appliances
- Topic: Single Phase Welders, let's get to the bottom of this
- Replies: 7
- Views: 38072
Re: Single Phase Welders, let's get to the bottom of this
WorkSafe - Energy Safety did something about this situation in 2021 and issued a prohibition on use of an adaptor/supply lead that allows a higher rated plug to be adapted down to a lower rated plug without inline protection. Sign up to the updates on their website, that's how they advise of things...
- Tue Oct 17, 2023 8:16 pm
- Forum: Appliances
- Topic: Single Phase Welders, let's get to the bottom of this
- Replies: 7
- Views: 38072
Re: Single Phase Welders, let's get to the bottom of this
I expect that tally-plate rating of 14.4 A will be the max continuous load, ie at 100 % duty cycle. The unit won't be able to draw 23.8 A continuously. Yet, that is the input current my welder is drawing, during a steady bead placement, maybe the thing is faulty, but it does good welds. :D Also the...
- Fri Dec 09, 2022 8:30 pm
- Forum: Earthing and Bonding
- Topic: Do I need to provide certification if I only install earths?
- Replies: 7
- Views: 50746
Re: Do I need to provide certification if I only install earths?
JamieP,
What sort of explosive dust are we talking here?
Is this some sort of an extraction system?
Also, what sort of length of run are we talking?
Cheers,
Mike T.
What sort of explosive dust are we talking here?
Is this some sort of an extraction system?
Also, what sort of length of run are we talking?
Cheers,
Mike T.
- Fri Dec 09, 2022 8:08 pm
- Forum: Off Topic/General Electrical Discussions
- Topic: EWRB COC Audits?
- Replies: 2
- Views: 18598
EWRB COC Audits?
Hi Guys. I remember back when Self-certification came in in 1992, the ERWB were hot on auditing the CoC's of people working in the trade. Over the years, this seems to have calmed down a bit. I can't remember the last time I got an e-mail from the Board that they wanted to see CoC's from such and su...
- Fri Dec 09, 2022 7:49 pm
- Forum: Appliances
- Topic: Single Phase Welders, let's get to the bottom of this
- Replies: 7
- Views: 38072
Re: Single Phase Welders, let's get to the bottom of this
Hey thanks AlecK, That has cleared up a lot of things for me. Being a qualified welder myself, before having got into the electrical trade, I have a single phase TIG welder here at home that draws 23.8A at full noise (200A output), this had a 15A plug on it when bought from new, 5 years ago, althoug...
- Mon Dec 05, 2022 10:27 pm
- Forum: Standards and Legislation
- Topic: Employer held responsible for workers transposition
- Replies: 3
- Views: 9041
Re: Employer held responsible for workers transposition
3 words, Un-identified aluminium conductors. The fact that there were two black sheathed conductors should have alerted the Electrician that this was going to be a polarity nightmare. Also the fact that WorkSafe flexed their muscles in this case is quite worrying and went over and above what the EWR...
- Mon Dec 05, 2022 10:11 pm
- Forum: Damp Situations
- Topic: exhaust fan in shower
- Replies: 9
- Views: 46170
Re: exhaust fan in shower
I would also make that fan an SELV fan, not mains voltage.
Run off of a transformer in the roof.
Run off of a transformer in the roof.
- Mon Dec 05, 2022 10:01 pm
- Forum: Apprentices and training
- Topic: is it ok for apprentices to work alone?
- Replies: 6
- Views: 40481
Re: is it ok for apprentices to work alone?
It also depends on the apprentice. Some people pick things quite easily, others not so. Those are the people that need to be supervised well. There was an apprentice a few years back found dead in a trench with a set of Duspols beside him, when he was working on an underground cable. This is why we ...
- Mon Dec 05, 2022 9:31 pm
- Forum: Appliances
- Topic: Single Phase Welders, let's get to the bottom of this
- Replies: 7
- Views: 38072
Single Phase Welders, let's get to the bottom of this
Hi Guys, As an Electrician, I do testing and tagging in a few places, because I can, it is pretty soul-destroying but it pays the bills. Now, every time I test and tag a couple of places, the welders (mainly MIG and Stick) have got 15A plug-tops attached to them because the company that services the...
- Mon Dec 05, 2022 8:54 pm
- Forum: General Electrical Discussions
- Topic: Strip Connector Busbar?
- Replies: 3
- Views: 22925
Re: Strip Connector Busbar?
For the Wiedmuller ones and the Legrand ones, they have screw links between the middle of the terminals, where the terminals fit to a DIN Rail.
I have no idea why in this day and age you would use wire links between terminals, in this situation.
I have no idea why in this day and age you would use wire links between terminals, in this situation.
- Mon Dec 05, 2022 8:43 pm
- Forum: Protective Devices
- Topic: Lock dogs for Rotary CB's ?
- Replies: 0
- Views: 19127
Lock dogs for Rotary CB's ?
Hi Guys, May I please ask what you guys are using to lock-out circuits that use the rotary type circuit-breakers. The type that I'm asking about are the Siemens Sirius gear where they don't have a hole in the actuator to put a padlock through. These are normally the lower current types (as in 6-20A)...
- Mon Dec 05, 2022 8:28 pm
- Forum: Protective Devices
- Topic: PDL breakers
- Replies: 3
- Views: 22228
Re: PDL breakers
Hi there guys, These are almost similar to the old "Quicklag" breakers that used to be fitted in the older Gael switchboards. I had to remove one of them elderly units last week as the fuse-switch unit at the bottom had failed destructively at 5 am. I'm surprised that there are any of these still ar...
- Thu Oct 06, 2022 7:52 pm
- Forum: Appliances
- Topic: Motor Isolation Switch
- Replies: 3
- Views: 21909
Re: Motor Isolation Switch
Suffice to say AlecK,
The protection only protects the cable running to the motor or the drive supplying it, not the motor itself.
The protection only protects the cable running to the motor or the drive supplying it, not the motor itself.
- Wed Oct 05, 2022 7:57 pm
- Forum: General Electrical Discussions
- Topic: Aegis Test Equipment?
- Replies: 4
- Views: 25543
Re: Aegis Test Equipment?
Personally, After a month or three of mucking around with this company, don't bother buying anything off of them. That is really hard to say, given that most companies are only too happy to sell you their wares, this one isn't. I asked for a quote on getting an Insulation/RCD tester from them, never...
- Wed Oct 05, 2022 7:21 pm
- Forum: Off Topic/General Electrical Discussions
- Topic: EST license ..what certification can be signed off
- Replies: 3
- Views: 21103
Re: EST license ..what certification can be signed off
With an EST licence, it is always an Electrical Safety Certificate.
- Wed Oct 05, 2022 7:17 pm
- Forum: General Electrical Discussions
- Topic: Bootlace Ferrules on standard non-flexible cables
- Replies: 3
- Views: 21727
Re: Bootlace Ferrules on standard non-flexible cables
JamieP, Personally I've only ever used these ferrules on what you'd call flexible cables and multi-cores that have really fine wires, that could cause a short-circuit if one of the strands made it into an adjacent terminal during termination. This was the whole idea of the boot-lace ferrule back in ...
- Sun Jun 19, 2022 4:23 pm
- Forum: General Electrical Discussions
- Topic: Aegis Test Equipment?
- Replies: 4
- Views: 25543
Re: Aegis Test Equipment?
Any sort of response on this?
I was merely asking the question.
Cheers,
Mike T.
I was merely asking the question.
Cheers,
Mike T.
- Tue May 31, 2022 11:58 pm
- Forum: Appliances
- Topic: Motor - Low insulation resistance
- Replies: 6
- Views: 33022
Re: Motor - Low insulation resistance
Nah,
That's all good.
No-one like to be anywhere near anything that goes BANG when it's first turned on.
And my god that has happened a LOT of times in my years in the trade!
That's all good.
No-one like to be anywhere near anything that goes BANG when it's first turned on.

And my god that has happened a LOT of times in my years in the trade!
- Mon May 30, 2022 8:59 pm
- Forum: Appliances
- Topic: squirrel cage induction motor 50 hz 60 hz
- Replies: 2
- Views: 18071
Re: squirrel cage induction motor 50 hz 60 hz
Hi Guys, I work on motors that are inherently controlled by VFD's (or VSD's, if you want to call them that). Most of the stuff is pumps for liquids, if you go below 30Hz with any type of pump, it will not move any liquid and you have cavitation issues as well. If however, you run a pump that is mean...
- Mon May 30, 2022 8:42 pm
- Forum: Apprentices and training
- Topic: Procedural Document
- Replies: 3
- Views: 23104
Re: Procedural Document
That is not the direction we want to go down here.
Making DIYer How-to's, is just wrong.
Making DIYer How-to's, is just wrong.
- Mon May 30, 2022 8:37 pm
- Forum: Appliances
- Topic: Motor - Low insulation resistance
- Replies: 6
- Views: 33022
Re: Motor - Low insulation resistance
Asked to connect a motor. This was a used motor so I checked the winding resistances, insulation resistance between windings and IR from windings to frame. My IRs were around 0.5M through to around 2.5M at the highest. I decided I wasn't happy to connect. My question is was this a fair judgement? I...
- Mon May 30, 2022 8:07 pm
- Forum: Off Topic
- Topic: HRV near bathroom fan
- Replies: 4
- Views: 30059
Re: HRV near bathroom fan
Hi Guys, I've seen a lot of this in the last few years, mainly with respect to range-hoods that are supposed to be vented through the roof or out through the wall adjacent to the hob/stove. Usually the excuse is that the "person" couldn't find the correct transition fitting to go from rectangular to...
- Mon May 30, 2022 7:41 pm
- Forum: General Electrical Discussions
- Topic: Aegis Test Equipment?
- Replies: 4
- Views: 25543
Aegis Test Equipment?
Hey Guys, What are your thoughts on this sort of test gear? I was wondering (having never bought this brand before) if it is any good. I'm after a Loop Impedance tester and this one seemed to be the goods: https://www.aegis.net.nz/products/electrical-testers/cz20054 Now, I already own a Megohm-meter...
- Mon May 30, 2022 7:14 pm
- Forum: General Electrical Discussions
- Topic: Bootlace Crimpers - Hex vs Square
- Replies: 3
- Views: 21817
Re: Bootlace Crimpers - Hex vs Square
Hey Guys, You really get what you pay for with this sort of thing. I did controls wiring for years with just the ratchet scissor type, never again, once the jaws start to wear and don't give a perfect crimp anymore, in the bin they go. We had issues with the wires merely falling out of bootlaces tha...