Peak output on the inverter is 9000 watts, so close to 40 amps, it is a 16mm neutral screen to house so that will be fine but the hot water cylinder is 2.5mm so will fuse it (easier to change size if it becomes and issue).
Thanks very much.
Search found 3 matches
- Wed Sep 07, 2022 7:28 pm
- Forum: Generators and Solar
- Topic: Best Practice earth loop impedance B type C/B or fuses
- Replies: 7
- Views: 6780
- Tue Sep 06, 2022 7:24 pm
- Forum: Generators and Solar
- Topic: Best Practice earth loop impedance B type C/B or fuses
- Replies: 7
- Views: 6780
Re: Best Practice earth loop impedance B type C/B or fuses
Thanks AlecK very helpful I do not however want to protect the mains supply with an RCD as I am going to eventually run a hot water cylinder off the inverter during summer, so I could just install b type circuit breakers on the main cable and hot water circuit. I would probably however just put in f...
- Mon Sep 05, 2022 6:50 pm
- Forum: Generators and Solar
- Topic: Best Practice earth loop impedance B type C/B or fuses
- Replies: 7
- Views: 6780
Best Practice earth loop impedance B type C/B or fuses
I have a fully off grid set up, I have wired up the house and a solar company has done the Solar panels, battery and inverter. House is wired the same as you would if it was grid tied, except supplied by a sub board off the inverter. Although it does pass RCD tests, it does not pass the earth loop i...