Imported EV's

Hi All, Just wanting some advice regarding this IC-CPD I recently came across. This came supplied with the vehicle. It has a rating of 100v/200v, 12A. According to the guidelines this would not be acceptable as it's required to be labelled by the manufacturer as being compatible with a 230v 50Hz sup...
by Dano
Wed Jan 27, 2021 9:59 am
Forum: Selection and Installation of Wiring Systems
Topic: Heat pump , max demand calc
Replies: 6
Views: 3768

Re: Heat pump , max demand calc

Thanks Jamie,
No issue with the table, I'm more after what amperage to use from the heat pump specifications. Eg, A heat pump im looking at has both 'rated amps(17.5A)' and 'max amps(30A)' in their specs. Should we be basing the demand calcs on the 17.5 or 30A figure?
by Dano
Tue Jan 26, 2021 4:15 pm
Forum: Selection and Installation of Wiring Systems
Topic: Heat pump , max demand calc
Replies: 6
Views: 3768

Heat pump , max demand calc

Hi All, With large heat pumps and ducted systems over 10a, just curious as to whether we should be using 'running current' or 'max current' when calculating max demand on an installation. I've always gone with max current/worst case scenario, but wondering if I should just be going on running curren...
by Dano
Thu Jul 30, 2020 11:10 am
Forum: Selection and Installation of Wiring Systems
Topic: Max demand Table C1
Replies: 5
Views: 3189

Re: Max demand Table C1

Thanks Aleck, I thought that was how I read it, but it just didn't seem right to me, so started to doubt myself. I have looked at a few jobs lately where there is over 10kw of fixed space heaters getting installed, yet because each individual heater is less than 10A, they are calculated as just anot...
by Dano
Thu Jul 30, 2020 9:01 am
Forum: Selection and Installation of Wiring Systems
Topic: Max demand Table C1
Replies: 5
Views: 3189

Max demand Table C1

Hi All, Just trying to get my head around the wording in Table C1, load group D, in regards to space heating and working out the MD for the entire installation. Load group B(i) is for socket outlets not exceeding 10A and permanently connected electrical equipment not exceeding 10A and not included i...