Search found 11 matches

by JamesM
Tue Feb 20, 2024 2:11 pm
Forum: Generators and Solar
Topic: Earth wire type for PV Array
Replies: 17
Views: 5982

Re: Earth wire type for PV Array

Hi Jamie, I struggle to see how equipotential bonding wires are thought to be excluded from the definition of a PV array. Just look at the items that are excluded by the definition i.e. “PV Array foundation, tracking apparatus, thermal control and other such components”. Not one of these items are d...
by JamesM
Tue Nov 28, 2023 10:31 am
Forum: Generators and Solar
Topic: Generator set up
Replies: 6
Views: 2580

Re: Generator set up

Hi JamieP, Have you had a look at this document - https://www.resourcesregulator.nsw.gov.au/sites/default/files/documents/out10-2110-ees-014-technical-principles-for-the-use-of-stand-alone-generators-_version-2__5_.pdf While has no legal standing in NZ, the same standards are referenced (i.e. AS/NZS...
by JamesM
Thu Jul 27, 2023 8:26 am
Forum: Appliances
Topic: 60 Hertz Welding Generator
Replies: 1
Views: 1331

60 Hertz Welding Generator

There is a scenario where a 60 Hertz welding generator is being used and the mechanics want to power hand tools off it (mostly grinders). Is this permitted in NZ? ESR 29 (2) appears to permit this. Is there anything wrong with using this at 60 Hertz if the tools are rated for 60 Hertz and a non-stan...
by JamesM
Mon Jul 24, 2023 7:36 am
Forum: Inspection
Topic: ESR 78D (2)(c) Periodic Assessments in Quarries and Alluvial Mining
Replies: 3
Views: 1559

Re: ESR 78D (2)(c) Periodic Assessments in Quarries and Alluvial Mining

Hi JamieP,

The EWRB’s direction regarding the limits to electrical work appear to make it clear that an Inspector who does not have a Mining Endorsement cannot do the Inspection – see https://www.ewrb.govt.nz/for-registered ... s-of-work/ for Electrical Inspector section "j"
by JamesM
Tue Apr 11, 2023 2:30 pm
Forum: Electric Vehicles and Charging Systems
Topic: Tesla Gen.3 Wall Charger
Replies: 9
Views: 7095

Re: Tesla Gen.3 Wall Charger

Both 7.9.3 (domestic) & 7.9.4 (other) specify that the "subcircuit" shall be protected; and you can't provide this protection at the downstream end. Hi AlecK – I’m really curious as to why protection can’t be provided at the downstream end as long as it’s a single circuit without branches – along t...
by JamesM
Wed Dec 01, 2021 6:26 am
Forum: Testing & Verification
Topic: Motor Insulation Resistance test
Replies: 4
Views: 5642

Re: Motor Insulation Resistance test

Thanks for your thoughts/advice Gregmcc - it is a short length of cable 2 or 3m long
by JamesM
Tue Nov 30, 2021 12:24 pm
Forum: Earthing and Bonding
Topic: 5.7.5 Supplementary Equipotential Bonding
Replies: 4
Views: 4657

Re: 5.7.5 Supplementary Equipotential Bonding

Just had another look at the wording after being prompted by AlecK’s comment “In 5.7; two times are specified: 0.4 sec for sockets (and some other particular types of equipment), and 5 sec for any other circuit”, and was surprised that the wording may not be as clear cut as I initially suspected. I ...
by JamesM
Tue Nov 30, 2021 6:23 am
Forum: Testing & Verification
Topic: Motor Insulation Resistance test
Replies: 4
Views: 5642

Re: Motor Insulation Resistance test

The motor is a 37kW internally connected (delta) with three active conductors only (no neutral). Hence the motor lead on which the tests were done has three active conductors and earth. The test showed the same pattern regardless of whether it was conducted between red and earth, white and earth, or...
by JamesM
Mon Nov 29, 2021 6:38 am
Forum: Testing & Verification
Topic: Motor Insulation Resistance test
Replies: 4
Views: 5642

Motor Insulation Resistance test

I have an old ( 8y+) submersible pump motor that had been disconnected for more than 6 months. I wanted to check and see if it tested ok and so did an insulation resistance test between phase and earth. I was expecting to get a reading either good or bad, however something unexpected happened – the ...
by JamesM
Wed Mar 10, 2021 8:12 am
Forum: Earthing and Bonding
Topic: PELV Earthing
Replies: 7
Views: 6293

Re: PELV Earthing

Billq - I think your reference to clause 4.4.4.3 (iii) is actually 5.4.1.1(iii)
by JamesM
Wed Jul 08, 2020 9:23 am
Forum: Protective Devices
Topic: PDL breakers
Replies: 3
Views: 4829

PDL breakers

I came across these old PDL devices that I suspect are MCBs. Can anyone provide any information on them including what range they are from, are they MCBs and what fault currents they are rated for etc? Thanks in advance for any help!
PDL.jpg