Search found 914 matches

by AlecK
Mon Aug 16, 2021 8:41 am
Forum: Protective Devices
Topic: Oven replacement - RCD protection of socket outlet?
Replies: 7
Views: 8143

Re: Oven replacement - RCD protection of socket outlet?

You're replacing a fitting (a cooking appliance) with a similar fitting. Therefore you're maintaining the installation; working under ESR 59(3), with 3 options available - one of them being maintaining in original condition. What some people call "like for like"; although that term doesn't appear an...
by AlecK
Sun Aug 15, 2021 12:03 pm
Forum: Transportable Installations
Topic: Does rcds rule of 3000 apply?
Replies: 8
Views: 6223

Re: Does rcds rule of 3000 apply?

Correct; For a WoEF, only those matters covered in Part 1 or in AppC are relevant.
So the precise arrangement of any RCD protection that's present isn't a WoEF matter.
by AlecK
Sat Aug 14, 2021 11:13 am
Forum: Transportable Installations
Topic: Does rcds rule of 3000 apply?
Replies: 8
Views: 6223

Re: Does rcds rule of 3000 apply?

Not that they can't apply. Just that in practice they seldom do; because caravans / motorhomes generally only have one subcircuit. Other types of connectable installation (eg mobile shop / kitchen) may have more than one subcircuit, but are non-domestic. If a caravan / motorhome ever did have more t...
by AlecK
Fri Aug 13, 2021 12:43 pm
Forum: Distribution, Networks & Metering
Topic: Outbuilding definition
Replies: 3
Views: 4574

Re: Outbuilding definition

For purposes of '3000"; ESR 4 (2) specifies that a term used in a Standard has the meaning used in that Standard, unless either the Act or ESRs provide a different definition. There's no definition of 'outbuilding" in either the Electricity act or ESRs; so the word takes the meaning used in '3000". ...
by AlecK
Fri Aug 13, 2021 9:19 am
Forum: Transportable Installations
Topic: Does rcds rule of 3000 apply?
Replies: 8
Views: 6223

Re: Does rcds rule of 3000 apply?

Yes, clause 2.6.2.4 applies; because nothing in "3001" modifies any part of it. So you have to apply (a); and distribute lighting over more than one subcircuit - IF there is more than one subcircuit As you've note, (b) - the 3 subcircuit rule - only applies to "residential installations". In 2018 ed...
by AlecK
Thu Aug 12, 2021 9:52 am
Forum: Transportable Installations
Topic: Does rcds rule of 3000 apply?
Replies: 8
Views: 6223

Re: Does rcds rule of 3000 apply?

As per clause 1.2, rules of "3000" apply unless specifically modified by "3001".
Which particular RCD rule are you thinking of?
by AlecK
Tue Aug 10, 2021 5:21 pm
Forum: Standards and Legislation
Topic: How long do we have to issue a CoC?
Replies: 14
Views: 8141

Re: How long do we have to issue a CoC?

I think it was actually deliberate. No need to put a time limit because officially all that matters is that the CoC gets issued before connection happens. And they don't care who issues it; as long as someone accepts responsibility. For larger contract-type jobs it's better this way, we wouldn't wan...
by AlecK
Tue Aug 10, 2021 12:35 pm
Forum: Selection and Installation of Wiring Systems
Topic: Shipping Container
Replies: 3
Views: 2032

Re: Shipping Container

Imported to NZ by:
https://digitalimports.co.nz
by AlecK
Tue Aug 10, 2021 9:08 am
Forum: Selection and Installation of Wiring Systems
Topic: Shipping Container
Replies: 3
Views: 2032

Re: Shipping Container

Whether you need to apply "3001" depends on whether the unit is to be plugged in ( transportable), or hard-wired as part (or all) of a fixed installation. If it's to be plugged in, then it must comply with Part 2 of "3000, as modified by "3001". Assuming it's a steel container, rather than an insula...
by AlecK
Mon Aug 09, 2021 3:51 pm
Forum: Standards and Legislation
Topic: How long do we have to issue a CoC?
Replies: 14
Views: 8141

Re: How long do we have to issue a CoC?

You can only be taken to task for doing, or not doing, something you have a duty to do / not do. If someone issues a CoC (or RoI, ir ESC), then they are responsible for validity of all the info it contains. For RoIs & ESCs there's a duty imposed on a particular individual to issue. But there's no su...
by AlecK
Mon Aug 09, 2021 10:36 am
Forum: Standards and Legislation
Topic: How long do we have to issue a CoC?
Replies: 14
Views: 8141

Re: How long do we have to issue a CoC?

Noting that EWRB recently "convicted" someone for failing-to certify.
Seems they - and their lawyers - have also failed to notice that there is no requirement placed on any person to issue a CoC
by AlecK
Mon Aug 09, 2021 10:33 am
Forum: Standards and Legislation
Topic: How long do we have to issue a CoC?
Replies: 14
Views: 8141

Re: How long do we have to issue a CoC?

No.
The offence would be connecting without sighting a CoC (and RoI if req'd).
Which is something that networks do all the time - and get away with 'cos nobody complains.
by AlecK
Mon Aug 09, 2021 10:25 am
Forum: Damp Situations
Topic: Shower with screen, zone 2
Replies: 8
Views: 7459

Re: Shower with screen, zone 2

Correct WRT title of 6.8, my error. For barrier height, it's clear that a (qualifying) barrier limits Z1 even above the top of the barrier. Which is logical because shower water generally sprays down rather than up And I believe that, since the Figs are intended to illustrate the rules of the clause...
by AlecK
Mon Aug 09, 2021 9:18 am
Forum: Standards and Legislation
Topic: How long do we have to issue a CoC?
Replies: 14
Views: 8141

Re: How long do we have to issue a CoC?

Yes, it certainly is PEW And being installation work, is at least general PEW; so a CoC is definitely required by ESR 65. Where work is incomplete, or where it was only intended as provision-for-later; whatever was done should be certified, but with care: - the description of work needs to be carefu...
by AlecK
Sun Aug 08, 2021 12:30 pm
Forum: Protective Devices
Topic: Oven replacement - RCD protection of socket outlet?
Replies: 7
Views: 8143

Re: Oven replacement - RCD protection of socket outlet?

Just a flaw; and - as you've noticed - corrected in 2018 edition.

On the other hand, that Exception was only ever intended for larger appliance, particularly ranges, due to the poor seals on older MIMS elements.
There's no good reason to avoid RCD for an oven.
by AlecK
Sun Aug 08, 2021 12:25 pm
Forum: Standards and Legislation
Topic: How long do we have to issue a CoC?
Replies: 14
Views: 8141

Re: How long do we have to issue a CoC?

Correct that work isn't completed until certified. and that once a CoC is issued; 74E then starts a timer for provision of copies. But there is no time limit for issue. And there's also nothing that makes it anyone's responsibility to issue; or even to ensure that a CoC is issued at all. What drives...
by AlecK
Fri Aug 06, 2021 12:15 pm
Forum: Damp Situations
Topic: Shower with screen, zone 2
Replies: 8
Views: 7459

Re: Shower with screen, zone 2

While most people rely on the Figs; what really matters is the words in the relevant clause. Especially the words that point to the Fig. Some Figs do introduce requirements that aren't in a clause, but this is regarded as poor practice when writing a Standard. The default position is that Figs illus...
by AlecK
Fri Aug 06, 2021 9:21 am
Forum: Switchboards
Topic: Restricted Locations - 2.9.2.5 (c)
Replies: 2
Views: 4896

Re: Restricted Locations - 2.9.2.5 (c)

For terms used in a standard, ESR 4(2) governs definitions. However neither "room" nor "cupboard" is defined in Act, or Regulations, or "3000"; or IEC60050. That means normal dictionary definitions should apply; buit as you suggest this could be open to interpretation. In my view, with more than 600...
by AlecK
Mon Aug 02, 2021 9:23 am
Forum: Appliances
Topic: Motor Overload - 4.13.2
Replies: 2
Views: 4226

Re: Motor Overload - 4.13.2

Doesn't say "individual" or "dedicated" or "separate" means of protection;
or any other wording that would require the protection for one motor to be only for that motor.

Not unheard of for several motors of a system to share common control / protection devices,
but needs care to get it right
by AlecK
Sun Jul 18, 2021 12:19 pm
Forum: Protective Devices
Topic: 2.6.3.1 Exception 3 - Can you apply this to gas appliances?
Replies: 3
Views: 4280

Re: 2.6.3.1 Exception 3 - Can you apply this to gas appliances?

The original reason for a provision isn't always obvious - but there usually is one. And yes, the words do matter. Both the words that are used, and the words that could have been but weren't. Something that should be taught as a subject for all electrical trainees (and other trainees for jobs that ...
by AlecK
Sat Jul 17, 2021 12:03 pm
Forum: Protective Devices
Topic: 2.6.3.1 Exception 3 - Can you apply this to gas appliances?
Replies: 3
Views: 4280

Re: 2.6.3.1 Exception 3 - Can you apply this to gas appliances?

I wouldn't classify any appliance that uses gas as the source of cooking heat as an "electric cooking appliance". They are gas cooking appliances. This Exception was created because - historically - the MIMS elements of electric cooking appliances tended to absorb atmospheric moisture if unused for ...
by AlecK
Mon Jul 12, 2021 10:54 am
Forum: Protective Devices
Topic: Minimum of two RCDs when more than one FSC 2.6.2.4 (b) (ii)
Replies: 3
Views: 4734

Re: Minimum of two RCDs when more than one FSC 2.6.2.4 (b) (ii)

First the question WRT whether the rule applies to number if subcircuits in swbd, or in installation. Easy answer; in the opening sentences: for option (a): "In all electrical installations where" for option (b): "In residential installations". These openings clearly tie the 'trigger' conditions tha...
by AlecK
Mon Jul 12, 2021 10:33 am
Forum: Generators and Solar
Topic: Section 4.5 - 4777.1-2016
Replies: 11
Views: 8682

Re: Section 4.5 - 4777.1-2016

Yes , could do a Part 1 CD - but as you say not for anything required to be fully Part 2
by AlecK
Wed Jul 07, 2021 10:30 am
Forum: Generators and Solar
Topic: 200Kva Generator Wash Plant
Replies: 3
Views: 4353

Re: 200Kva Generator Wash Plant

As a fixed installation, the main applicable Standard is "3000". As non-domestic, choice of Part 1 or Part2; but if it was Part 1 you wouldn't be asking the questions because all this would be part of the certified design. As a Part 2 installation; earthing requirements are set in Section 5; but may...
by AlecK
Wed Jul 07, 2021 9:39 am
Forum: Generators and Solar
Topic: Section 4.5 - 4777.1-2016
Replies: 11
Views: 8682

Re: Section 4.5 - 4777.1-2016

So far we've been discussing the requirements set in 2016 edition; which is not the edition cited in ESRs. Looking at cited 2005 edition; the relevant clause [5.4] is much simpler. An isolation device (not necessarily a switch) must be provided between the energy source and the inverter, unless the ...
by AlecK
Tue Jul 06, 2021 4:12 pm
Forum: Generators and Solar
Topic: 200Kva Generator Wash Plant
Replies: 3
Views: 4353

Re: 200Kva Generator Wash Plant

Fixed installation?
Or mobile / relocatable?

This determines which Standards apply
And in turn that determines the earthing arrangements
by AlecK
Tue Jul 06, 2021 9:24 am
Forum: Transportable Installations
Topic: Inverters
Replies: 1
Views: 2850

Re: Inverters

It's not a matter of Brands; it's a matter of how the output is configured. The inverter provided is not suitable; as it does not have an acceptable output earthing configuration. There's also a good chance that it is a transformerless type; bringing the risk that an internal fault could liven the b...
by AlecK
Mon Jul 05, 2021 4:54 pm
Forum: Earthing and Bonding
Topic: Requirements for screens of cables for interference
Replies: 3
Views: 4982

Re: Requirements for screens of cables for interference

more that it's not part of the installation in many (most (?) cases. ("installation wiring" being only part of what is within Scope; there's also 'equipment wiring" that can be part of the installation.) Instrumentation, like fire alarm, burglar alarm, TV, telephone, & data cabling generally aren't ...
by AlecK
Mon Jul 05, 2021 9:13 am
Forum: Earthing and Bonding
Topic: Requirements for screens of cables for interference
Replies: 3
Views: 4982

Re: Requirements for screens of cables for interference

Many such cables are not within scope of Wiring Rules; and therefore the requirements for ID of conductor function do not apply. Where Wiring Rules do apply, then yes any earthing for other than safety purposes is functional earthing. Definition 1.4.66 applies; but in my view doesn't make the necess...
by AlecK
Mon Jul 05, 2021 8:39 am
Forum: Generators and Solar
Topic: Section 4.5 - 4777.1-2016
Replies: 11
Views: 8682

Re: Section 4.5 - 4777.1-2016

Agree the input voltage level doesn't determine whether the Standard applies; It applies due to the output being grid-connected. And ESR 60 takes that another step, by making compliance with the Standard mandatory (if following Part 2 of 3000). Unfortunately none of this helps with your original que...
by AlecK
Fri Jul 02, 2021 10:42 am
Forum: Generators and Solar
Topic: Section 4.5 - 4777.1-2016
Replies: 11
Views: 8682

Re: Section 4.5 - 4777.1-2016

One Standard is not supposed to set requirements for matters outside its Scope, and within the Scope of another Standard. But many do - as in this case. 4777 cannot actually impose a requirement for anything to do with the PV array. It can however come close; by (a) setting a conditional requirement...
by AlecK
Thu Jul 01, 2021 9:03 am
Forum: Generators and Solar
Topic: Section 4.5 - 4777.1-2016
Replies: 11
Views: 8682

Re: Section 4.5 - 4777.1-2016

Can't "just" follow 5033; because that para is not written as an Exception but rather as an additional requirement.
So have to comply with both.
by AlecK
Sun Jun 27, 2021 10:25 am
Forum: Generators and Solar
Topic: Single phase generator on a 3 phase installation
Replies: 6
Views: 7537

Re: Single phase generator on a 3 phase installation

There was an amendment to "3010: 2017"; to correct a number of errors An outline has been prepared for restructuring the document, with intent to set up an amendment / revision project; but not yet confirmed and converted to a formal "project proposal". The project proposal sets limits to what can a...
by AlecK
Sat Jun 26, 2021 3:46 pm
Forum: Generators and Solar
Topic: Single phase generator on a 3 phase installation
Replies: 6
Views: 7537

Re: Single phase generator on a 3 phase installation

What it doesn't say is 'all active conductors everywhere'. And it doesn't say "all active conductors of all normal supplies". In many installations there will be multiple main switches, feeding various parts / sections of the installation; as illustrated in Fig 7.1. If you're providing alt supply fo...
by AlecK
Sat Jun 26, 2021 12:25 pm
Forum: Generators and Solar
Topic: Single phase generator on a 3 phase installation
Replies: 6
Views: 7537

Re: Single phase generator on a 3 phase installation

No problem in principle with having an alternative supply for only part of an installation. Just have to follow the basic principles; including no back-feed from alt supply to normal supply source. Yes if you simply switched one incoming phase of normal supply, and it normally fed any loads that wer...
by AlecK
Fri Jun 25, 2021 11:56 am
Forum: Selection and Installation of Wiring Systems
Topic: 2 phase current calculation
Replies: 2
Views: 2229

Re: 2 phase current calculation

I would treat this as a single-phase calculation. Adding the extra phase will result in N-current being less than the sum of phase currents, and therefore less contribution to volt-drop from the N; but to determine how much less you have to do a separate calculation for the N. Which is difficult sin...
by AlecK
Fri Jun 18, 2021 10:38 am
Forum: Switchboards
Topic: Submain configuration
Replies: 4
Views: 5614

Re: Submain configuration

Yes this requirement is specifically stated for PEN conductors passing through one DB on their way to another. And true it's not stated directly for common submains that similarly pass through an intermediate DB. But it's a result of the definition I mentioned - though maybe i wasn't clear enough WR...
by AlecK
Fri Jun 18, 2021 10:00 am
Forum: Forum User Guidelines
Topic: Switch Socket Outlets on different phases in same room
Replies: 3
Views: 8583

Re: Switch Socket Outlets on different phases in same room

- earth fault on item 1 - open-circuit PEC in item 1 - earth fault on item 2 - open-circuit PEC in item 2 That's not just 4 simultaneous faults; but a particular combination of faults. Plus a fifth condition: that the two items are simultaneously accessible. It's true this scenario could result in a...
by AlecK
Wed Jun 16, 2021 8:32 am
Forum: Forum User Guidelines
Topic: Switch Socket Outlets on different phases in same room
Replies: 3
Views: 8583

Re: Switch Socket Outlets on different phases in same room

There isn't any. And the scenario proposed, of a hazard arising from two Class I single phase appliances plugged into different phases , and with simultaneous earth fault isn't valid. Assuming the normal fault protection by automatic disconnection, then for each appliance the disconnection occurs wi...
by AlecK
Tue Jun 15, 2021 8:57 am
Forum: Selection and Installation of Wiring Systems
Topic: Overload Protection
Replies: 5
Views: 3172

Re: Overload Protection

We use these Exceptions so often that we tend to forget that they are Exceptions.
by AlecK
Mon Jun 14, 2021 11:39 am
Forum: Switchboards
Topic: Switchboard access changes due to AS/NZS 3000-2018 Amendment 2
Replies: 4
Views: 16473

Re: Switchboard access changes due to AS/NZS 3000-2018 Amendment 2

True in 2000 edition the "access' and 'egress' requirements were in different clauses. And true in that edition there was a 0.6 m requirement "around switchboards' that was under the "emergency exit" heading. Nothing about open doors etc. Also nothing at all to explain what "adequate space' for acce...
by AlecK
Mon Jun 14, 2021 9:52 am
Forum: Switchboards
Topic: Switchboard access changes due to AS/NZS 3000-2018 Amendment 2
Replies: 4
Views: 16473

Re: Switchboard access changes due to AS/NZS 3000-2018 Amendment 2

Can only approach this in [NZ] context; as i have no experience or detailed knowledge of earlier [A] only Wiring Rules
by AlecK
Mon Jun 14, 2021 9:48 am
Forum: Selection and Installation of Wiring Systems
Topic: Overload Protection
Replies: 5
Views: 3172

Re: Overload Protection

First the rules as they are now for new work. Correct that the default requirement [2.5.1.2]is overcurrent protection (both overload and short circuit) at origin of circuit; and at each reduction of CCC . Three Exceptions listed, with "pointers" to the relevant details (which are in following clause...
by AlecK
Fri Jun 11, 2021 10:13 am
Forum: Testing & Verification
Topic: 115V P-e, N-e, 240V P-N
Replies: 7
Views: 7154

Re: 115V P-e, N-e, 240V P-N

That fail is simply because - as you already established - the voltage A-E is only 115 V As such; an EFLI tester designed for 230 V will not commence the test. An EFLI tester works by applying a known resistor across a measured voltage for a limited time; in order to then calculate the impedance of ...
by AlecK
Thu Jun 10, 2021 10:59 am
Forum: Testing & Verification
Topic: 115V P-e, N-e, 240V P-N
Replies: 7
Views: 7154

Re: 115V P-e, N-e, 240V P-N

Those readings are typical of a supply from a 2-phase 180 degree supply, eg from an genset with "centre-tapped" winding. Assuming this is on an MEN supply; that is probably coincidence. But it shows that leaping to the "obvious" conclusion isn't a valid fault-finding technique. So far you know the d...
by AlecK
Tue Jun 08, 2021 2:28 pm
Forum: Selection and Installation of Wiring Systems
Topic: Submains though apartment ceilings
Replies: 1
Views: 1290

Re: Submains though apartment ceilings

From Wiring rules perspective; no problem with having wiring for one installation rune through part(s) of structure where another installation is located. And in this case, it's all same installation anyway. Being separate titles, likely an easement or equivalent arrangement will be needed , for any...
by AlecK
Fri Jun 04, 2021 8:50 am
Forum: Switchboards
Topic: Main switch board under stairs by only exit (fire exit)
Replies: 7
Views: 8139

Re: Main switch board under stairs by only exit (fire exit)

I think that's a reasonable approach.
by AlecK
Thu Jun 03, 2021 4:57 pm
Forum: Selection and Installation of Wiring Systems
Topic: Green only heat shrink for earth's
Replies: 6
Views: 2992

Re: Green only heat shrink for earth's

I suppose you have to do what the boss wants.
Unless it is non-compliant.
by AlecK
Thu Jun 03, 2021 2:45 pm
Forum: Switchboards
Topic: Main switch board under stairs by only exit (fire exit)
Replies: 7
Views: 8139

Re: Main switch board under stairs by only exit (fire exit)

I agree that a person carrying out inspection has a moral obligation to provide advice to installers, even for matters outside the strict limits of the high risk PEW they have been contracted to inspect. Energy Safety (Worksafe) have made it clear that they see Inspectors as having a mentoring role ...
by AlecK
Thu Jun 03, 2021 10:08 am
Forum: Transportable Installations
Topic: Shore power connector & inlet
Replies: 12
Views: 6943

Re: Shore power connector & inlet

Since this boat has an on-board tx; the only relevant clause is 5.5.6. Neither your post nor Camel007's includes any justification for preferring the tx case be earthed to boat's earthing system'; which is contrary to the underlying requirement of AS/NZS 3000 that it be earthed to the circuit that s...