Re: Steel bench top.

protective earthing [5.2.1] is not required. the bench is not any of the things that is required to be earthed for fault protection by automatic disconnection of supply [5.4] It's not exposed conductive parts of electrical equipment [5.4.1.1], nor conductive building materials [5.4.1.2] . Even if it...
by AlecK
Mon Mar 01, 2021 10:31 am
Forum: Selection and Installation of Wiring Systems
Topic: Cable Duct vs Conduit
Replies: 4
Views: 2493

Re: Cable Duct vs Conduit

If it isn't clearly marked with both duty and Standard; I wouldn't use it underground.
Or at least, not for LV installation wiring where the category depends on the duct / conduit.
by AlecK
Mon Mar 01, 2021 10:28 am
Forum: General Electrical Discussions
Topic: Analog vs Digital Insulation Resistance Testers
Replies: 1
Views: 3964

Re: Analog vs Digital Insulation Resistance Testers

I have both types. Also an older hand-cranked analogue, now only for workshop use. "Horses for courses." If I want to record test values - which isn't often, 'cos it slows you down - I might use the digital; because it's easier to read the digits than to read off a scale. But I prefer my analogue IR...
by AlecK
Mon Mar 01, 2021 9:37 am
Forum: General Electrical Discussions
Topic: PSOA questions
Replies: 6
Views: 8639

Re: PSOA questions

There's a lot of stuff available for sale that is inherently not fit for use and bordering on electrically unsafe. Like other connector Standards, '3112" specifies the details for plugs , sockets, connectors, etc so that they all match. In fact cord connectors for our three-pin, flat-pin LV are spec...
by AlecK
Sun Feb 28, 2021 9:06 am
Forum: Transportable Installations
Topic: WoEF - No Overload Protection in Caravan
Replies: 13
Views: 5704

Re: WoEF - No Overload Protection in Caravan

Pluto's very detailed history is - mostly - correct. Not that it changes anything, as we'd already reached the conclusions that a) the set-up was non-compliant and couldn't be issued a WoEF ; and b) it may well have complied when installed, under ECP 1. Pluto disagrees with conclusion b), and states...
by AlecK
Sat Feb 27, 2021 1:00 pm
Forum: Earthing and Bonding
Topic: Pool Equipment Bonding 5.6.2.6.1 (b)
Replies: 6
Views: 6206

Re: Pool Equipment Bonding 5.6.2.6.1 (b)

I think what you're missing is that this bonding is not related to hazards arising from the electrical equipment. It's about hazards arising from the pool water being at significantly different earth potential than the installation's earthing system. In crude terms, and for an extreme case, the pool...
by AlecK
Fri Feb 26, 2021 3:43 pm
Forum: Selection and Installation of Wiring Systems
Topic: Cable Duct vs Conduit
Replies: 4
Views: 2493

Re: Cable Duct vs Conduit

It should have the Standard it's made to comply with printed on it. 2053 series for plastic conduits. I suspect ducts is the same standard, with "duct" being used more as general size indicator Agree for Cat A needs to be HD, or MD encased in concrete (assuming plastic duct and insulated / sheathed ...
by AlecK
Fri Feb 26, 2021 1:52 pm
Forum: Selection and Installation of Wiring Systems
Topic: Overhead Submain Cabling
Replies: 17
Views: 7835

Re: Overhead Submain Cabling

Exactly. 3.12.4 is about distance between supports. Yes there's a difference between the max distance between supports for annealed Cu (20 m) and hard drawn (40 m for 2 conductors 6 mm2, 60 m for 16 mm2 and greater) . Which shows that yes longer spans of copper need to be HD. And also shows that the...
by AlecK
Fri Feb 26, 2021 1:26 pm
Forum: Earthing and Bonding
Topic: Pool Equipment Bonding 5.6.2.6.1 (b)
Replies: 6
Views: 6206

Re: Pool Equipment Bonding 5.6.2.6.1 (b)

True the PECs we install primarily for purposes of fault protection can also serve an equipotential bonding function. So yes, if the pool equipment is Class I and so has a PEC; then the PEC can also act as a EBC (and because incorporated into the cable instead of being a separate conductor, doesn't ...
by AlecK
Fri Feb 26, 2021 11:22 am
Forum: Transportable Installations
Topic: WoEF - No Overload Protection in Caravan
Replies: 13
Views: 5704

Re: WoEF - No Overload Protection in Caravan

One option would be to restore the unit to compliance with original rules; ie ECP1. However that's only short-term solution; as eventually the WoEF system will change so that N-E links have to be removed and RCd + current limitation has to be fitted before a WoEF can be issued. (being written into n...
by AlecK
Thu Feb 25, 2021 11:07 pm
Forum: Transportable Installations
Topic: WoEF - No Overload Protection in Caravan
Replies: 13
Views: 5704

Re: WoEF - No Overload Protection in Caravan

Exactly.

However it's possible this unit is old enough to have originally had a N-E link that has since been (illegally) removed.
Under ECP 1 allowed the link to be at the first fitting if there was no switchboard;
and that arrangement was not uncommon ('cos it was cheaper)
by AlecK
Thu Feb 25, 2021 10:58 pm
Forum: Selection and Installation of Wiring Systems
Topic: Overhead Submain Cabling
Replies: 17
Views: 7835

Re: Overhead Submain Cabling

Table 3.9 does NOT specify that hard drawn must be used.
The table specifies the maximum spans for various types of cable; and the longest span - 60 m - can apply to several types; not all of which are hard drawn.
by AlecK
Tue Feb 23, 2021 3:24 pm
Forum: Transportable Installations
Topic: Imported caravan COC or EWOF
Replies: 4
Views: 2469

Re: Imported caravan COC or EWOF

If it has been built to NZ requirements; then that's ESR 60(1)((e) which requires full compliance with "3000" as modified by "3001" (and that's what a CoC would be certifying). Which - as you've noted - means that sockets generally need a control switch - not necessarily integral - to comply with 4....
by AlecK
Tue Feb 23, 2021 10:00 am
Forum: Transportable Installations
Topic: Imported caravan COC or EWOF
Replies: 4
Views: 2469

Re: Imported caravan COC or EWOF

CoCs are for work done under NZ law; which is generally work done in NZ. A CoC doesn't have to be issued for an imported connectable installation that was wired overseas; though there's nothing to prohibit one from being issued. In many places the wiring of caravans etc is not done as electrical wor...
by AlecK
Tue Feb 23, 2021 9:38 am
Forum: Selection and Installation of Wiring Systems
Topic: Overhead Submain Cabling
Replies: 17
Views: 7835

Re: Overhead Submain Cabling

Rather than risk chasing down off-topic rabbit-holes; I'll avoid the (non) issue of "conductors" vs "cables" for now; other than simply observing that "cable" is a defined term [1.4.17], and that every cable has at least one conductor. There are several options for the original situation [Residentia...
by AlecK
Mon Feb 22, 2021 4:51 pm
Forum: Selection and Installation of Wiring Systems
Topic: Overhead Submain Cabling
Replies: 17
Views: 7835

Re: Overhead Submain Cabling

3.13.3 says anything on catenary (outdoors) uses the clearances for N/S.
There's no height for TPS as aerial conductors; 'cos you just don't do it.
by AlecK
Mon Feb 22, 2021 4:40 pm
Forum: Standards and Legislation
Topic: Are DC + and - considered as "Active"s in 3000
Replies: 6
Views: 3181

Re: Are DC + and - considered as "Active"s in 3000

Refer definitions 1.4.101 vs 1.4.102; also clause 4.3 for demarcations between. These make it very clear for discrete items of equipment; but rather less clear for what might be called 'distributed equipment'. Example 1: split system heat pump. The supply to it, through the isolating switch req'd by...
by AlecK
Mon Feb 22, 2021 10:44 am
Forum: Selection and Installation of Wiring Systems
Topic: Overhead Submain Cabling
Replies: 17
Views: 7835

Re: Overhead Submain Cabling

Tails from o/h supply to mains entry box are not required to be double insulated; exactly the same rules apply to the tails as for the incoming aerial span. However the insulation material may well be different; therefore requiring different treatment. These days aerials are generally N/S rather tha...
by AlecK
Mon Feb 22, 2021 8:51 am
Forum: Standards and Legislation
Topic: Are DC + and - considered as "Active"s in 3000
Replies: 6
Views: 3181

Re: Are DC + and - considered as "Active"s in 3000

The colour codes specified in "3000" [3.8.1 / Table 3.4] apply only to "installation wiring". That includes the "absolute" ban [3.8.1 & 1.7.2] on green, yellow, or green-yellow for active or neutral. In most cases signal cables are not "installation wiring" . Where it is 'installation wiring", and c...
by AlecK
Thu Feb 18, 2021 2:04 pm
Forum: Appliances
Topic: Large induction hobs
Replies: 3
Views: 3958

Re: Large induction hobs

if the MIs just state a load current, then we can still apply diversity to FLC. But if MIs specify a cable size or circuit rating, then that would be the minimum; and the 2018 edition will require us to comply. Which can be a problem if the MIs are written for US market; where V is 110 & A for any g...
by AlecK
Thu Feb 18, 2021 1:40 pm
Forum: Selection and Installation of Wiring Systems
Topic: Overhead Submain Cabling
Replies: 17
Views: 7835

Re: Overhead Submain Cabling

TPS on catenary doesn't need conduit.

(use 3.13 catenary instead of 3.12 aerial)
by AlecK
Thu Feb 18, 2021 9:58 am
Forum: Standards and Legislation
Topic: Are DC + and - considered as "Active"s in 3000
Replies: 6
Views: 3181

Re: Are DC + and - considered as "Active"s in 3000

Yes (technically); for an un-earthed d.c. system Though note that in 2.3.2.1.1; which sets requirements for a.c & d.s systems; the words 'active" & "neutral" are used only for a.c. I suspect this is just the background bias towards LV a.c. that exists throughout "3000" I'll have to check what the IE...
by AlecK
Thu Feb 18, 2021 9:54 am
Forum: Standards and Legislation
Topic: Issuing a WoEF is not PEW
Replies: 1
Views: 1303

Re: Issuing a WoEF is not PEW

Yes, they got it wrong. Again. Detailed explanation can wait; but suffice to say that their classification of it as maintenance is fundamentally flawed, ; and appears to have been made principally so that they could apply disciplinary provisions (which can only apply to people doing PEW). If it's no...
by AlecK
Thu Feb 18, 2021 9:46 am
Forum: Switchboards
Topic: Main switch readily accessible exception
Replies: 11
Views: 9565

Re: Main switch readily accessible exception

The exception to 2.9.1 provides guidance. Also note the2.9.2.3 requirement for MSB to be "within easy access of an entrance". Also 2.9.2.4 requirements for door to MSB to be clearly marked; and for location of MSB to be indicated conspicuously at each entrance. It comes down to balancing the safety ...
by AlecK
Thu Feb 18, 2021 9:36 am
Forum: Transportable Installations
Topic: Switchboards in transportable structures
Replies: 1
Views: 1401

Re: Switchboards in transportable structures

This Clause only relates to location (of the control & protection items covered by clause 3.3); and the "treated as MSB" part (added in A1, Jun 2012) is clearly stated to be limited to "for the purposes of access". Other requirements for MSBs, or other swbds, do not apply - or rather, not via this c...
by AlecK
Thu Feb 18, 2021 9:22 am
Forum: Testing & Verification
Topic: CoV for 6mo+ Re-livening
Replies: 2
Views: 4334

Re: CoV for 6mo+ Re-livening

no, you're NOT allowed to cut those seals. And if you did; you'd be liable for the cost of having the metering re-certified. Which means you can't re-liven,Trustpower will have to do it which is why they need to "sight" the certificate (as per ESR 74) Similar if the isolation is by removal of servic...
by AlecK
Thu Feb 18, 2021 9:14 am
Forum: Testing & Verification
Topic: Testing after switchboard upgrade
Replies: 3
Views: 5140

Re: Testing after switchboard upgrade

1 megohm on 230V gives 0.23 mA . The 10k ohm allowed for eg MIMS elements gives 23 mA - usually but not always enough to trip a 30 mA RCD Conversely; 30 mA (RCD must trip) comes at 7667 ohms. so just how low was the reading? slightly above 0 ohm (as stated) should certainly result in RCD tripping Sl...
by AlecK
Thu Feb 18, 2021 8:54 am
Forum: General Electrical Discussions
Topic: History of 3000
Replies: 6
Views: 6998

Re: History of 3000

Publication / Gazette date is seldom the effective date. As a living document, ESRs are a composite, with changes made at infrequent intervals. Most significant chages are made by issuing "Amendment Regs, and these will include a date, or dates, that the amendments come into force.. EG the Electrici...
by AlecK
Thu Feb 18, 2021 8:35 am
Forum: Earthing and Bonding
Topic: Nominal size
Replies: 5
Views: 4395

Re: Nominal size

Agree with DougP that the tails may possibly be undersized. Not enough info given to be sure; as CCC depends not only on conductor material; but also insulation type, and installation conditions (for worst part of the run). however as long as they do have CCC adequate for load to be carried, and are...
by AlecK
Thu Jan 14, 2021 11:52 am
Forum: Inspection
Topic: VERIFICATION OF MARINE
Replies: 5
Views: 5374

Re: VERIFICATION OF MARINE

Not the same thing. A CoV is a hangover from 1993 Regs. There's no official, or example, RoA (yet) except in latest (2019 + A1) edition of "3012" Similar forms coming in current revisions of 3001 & 3004; the only differences being the Standard(s) referred to. But the basic requirements for an RoA ar...
by AlecK
Thu Jan 14, 2021 11:15 am
Forum: Standards and Legislation
Topic: ESR 73A (e)
Replies: 3
Views: 2188

Re: ESR 73A (e)

I suspect this requirement is mostly ignored. But yes, i believe that a visual check plus continuity test confirms that a MES exists. Nothing says it has to be off any particular standard or efficacy. Would have to think about alternative tests that might be deemed adequate if electrode not readily ...
by AlecK
Tue Jan 12, 2021 11:42 am
Forum: Inspection
Topic: VERIFICATION OF MARINE
Replies: 5
Views: 5374

Re: VERIFICATION OF MARINE

Looks nasty; whatever it's meant to be doing. The question of whether the "floating dock" is a boat or not doesn't really matter; as the fact that it's directly connected to an installation means it comes under the rules for that installation. It's acceptable to directly connect a boat, but doing so...
by AlecK
Tue Jan 12, 2021 10:45 am
Forum: Standards and Legislation
Topic: ESR 73A (e)
Replies: 3
Views: 2188

Re: ESR 73A (e)

In general we're only responsible for what we do, and not for what was already there (except that we mustn't make existing stuff any less safe than it was). Accordingly I believe the correct interpretation is that these pre-connection checks apply in terms of the supply to the "part installation" ab...
by AlecK
Mon Jan 11, 2021 1:43 pm
Forum: Earthing and Bonding
Topic: MEN Switchboards
Replies: 6
Views: 6469

Re: MEN Switchboards

"MEN" is a term used to describe the particular variant of the TN-C-S earthing system that is generally used for distribution in Oz & NZ. That is, the distribution system is TN-C; with the "multiple" points of tying the distribution N to earth being 1 at the transformer and one in each installation ...
by AlecK
Mon Jan 11, 2021 11:58 am
Forum: General Electrical Discussions
Topic: History of 3000
Replies: 6
Views: 6998

Re: History of 3000

For Regs, there's always a "commencement date", generally Reg 1 is "Title" & Reg 2 is "Commencement" . For ESRs 2010; it was given simply as 1 April 2010, so that one is easy. They don't change that Reg when amendments happen; but each amendment is published as a separate "Electricity (Safety) Amend...
by AlecK
Tue Jan 05, 2021 2:44 pm
Forum: Protective Devices
Topic: Redundant Isolation Switch in combination boards (meter + MSB)
Replies: 2
Views: 4463

Re: Redundant Isolation Switch in combination boards (meter + MSB)

The requirement for o/l protection may be spelt out in Orion's (and some other) network connection contracts; but it's always our responsibility because mains are part o9f the installation; and all conductors in the installation must have o/l protection, short circuit protection, & fault protection....
by AlecK
Tue Jan 05, 2021 1:57 pm
Forum: General Electrical Discussions
Topic: History of 3000
Replies: 6
Views: 6998

Re: History of 3000

Pluto's list includes an entry for "Electrical Regulations 2007 + AS/NZS 3000". No such Regulations were ever promulgated. The1993 Regs were issued under a significantly revised Electricity Act; so many of the changes related to aligning with that. The principal changes for Electricians related to t...
by AlecK
Tue Dec 29, 2020 10:13 am
Forum: Appliances
Topic: UK Downlights
Replies: 7
Views: 5480

Re: UK Downlights

Correct that SDoC is a control on what's for sale/supply, and has SFA to do with what gets installed / connected. Regardless of source. & regardless of SDoC / Approval; responsibility for everything that gets connected rests on the person who connects it. If connected by an electrician, there has to...
by AlecK
Mon Dec 28, 2020 9:02 am
Forum: Appliances
Topic: UK Downlights
Replies: 7
Views: 5480

Re: UK Downlights

The importer is whoever arranges for import; which in this case is the homeowner. I believe that no offence would be committed by anyone if such fittings were installed, either by homeowner or by an electrician. However it's likely an offence would be committed if the house was later sold while incl...
by AlecK
Sat Dec 26, 2020 1:05 pm
Forum: Protective Devices
Topic: Protective device disconnection times
Replies: 1
Views: 4632

Re: Protective device disconnection times

No; it doesn't mean that at all. The max acceptable disconnection times are set differently due to different levels of risk; as in there's much less risk of shock from fixed equipment than from portable equipment. This relates to providing "fault protection"; ie protection against shock from contact...
by AlecK
Fri Dec 25, 2020 2:58 pm
Forum: Earthing and Bonding
Topic: While you're waiting for your Christmas roast to cook..
Replies: 4
Views: 4100

Re: While you're waiting for your Christmas roast to cook..

So I'm not the only sad bugger who just had to check the forum today
by AlecK
Wed Dec 23, 2020 10:22 am
Forum: Switchboards
Topic: Switchboard Replacement - Incoming PEN and main earth same stud
Replies: 4
Views: 5222

Re: Switchboard Replacement - Incoming PEN and main earth same stud

ESR 113 doesn't apply when fittings are replaced. It's about items remaining in service ("may continue to be .... used"); and when you replace something it's not continuing to be used. You stop using the old and start using the new. The regulation that applies for replacement is ESR 59(3); which all...
by AlecK
Tue Dec 22, 2020 6:03 pm
Forum: Switchboards
Topic: Switchboard Replacement - Incoming PEN and main earth same stud
Replies: 4
Views: 5222

Re: Switchboard Replacement - Incoming PEN and main earth same stud

It's certainly not "maintaining" or "repairing"; as it changes the configuration of the way the installation's earthing is connected. It affects the MEC, so it's "mains work"; and as non-maintenance mains work ESR 6A classifies it as high risk PEW. As with any classification system, there are always...
by AlecK
Tue Dec 22, 2020 9:05 am
Forum: Inspection
Topic: Inspection after livening
Replies: 11
Views: 8863

Re: Inspection after livening

So the driveway has been concreted. That's NO reason not to inspect. In fact it is reason to be suspicious that the cable-laying isn't right. There's only two possible reasons why they didn't ask for inspection until this late. Either they're trying to hide something; or they are - as you suggest - ...
by AlecK
Sun Dec 20, 2020 7:48 am
Forum: Earthing and Bonding
Topic: Can earth electrode be installed next to gas cylinder
Replies: 2
Views: 3181

Re: Can earth electrode be installed next to gas cylinder

Short answer: No; because Schedule 2 of ESRs changes Clause 4.18
by AlecK
Sun Dec 20, 2020 7:45 am
Forum: Inspection
Topic: Inspection after livening
Replies: 11
Views: 8863

Re: Inspection after livening

Yes, an electrode is electrical equipment. It's not equipment that would be classed as a source of ignition; but while that wording is used in Clause 4.18; that';s not the rule we have to apply. Schedule 2 of ESRs changes this clause (and several others); so that only electrical equipment that is di...
by AlecK
Sun Dec 20, 2020 7:32 am
Forum: Standards and Legislation
Topic: Old House relocated
Replies: 6
Views: 3537

Re: Old House relocated

You are correct ; but only WRT the CoC, there's nothing about relying on the RoI.
and they also have to sight signed test results

(Sorry; I should have checked; never rely on memory)
by AlecK
Fri Dec 18, 2020 10:56 am
Forum: Inspection
Topic: Inspection after livening
Replies: 11
Views: 8863

Re: Inspection after livening

An interesting example; and I understand that yes, this sort of thing has been going on in the "deep south" for years. Until recently, with knowledge and support of the network; though that may now be changing. Certainly Powernet has tightened up on who can access the network assets under their cont...
by AlecK
Thu Dec 17, 2020 8:55 am
Forum: Standards and Legislation
Topic: AS/NZS 3000:2007 Superseded?
Replies: 9
Views: 4633

Re: AS/NZS 3000:2007 Superseded?

My understanding is that all industry orgs have repeatedly sought & supported the updating of citations. 3years ago MasterElectricians put a lot of effort into providing a nationwide roadshow covering changes in 2018 edition of "3000"; in expectation that the ESRs amendment would happen as previousl...
by AlecK
Wed Dec 16, 2020 3:54 pm
Forum: Electric Vehicles and Charging Systems
Topic: Isolation and Inspection
Replies: 3
Views: 4931

Re: Isolation and Inspection

The Guidelines are just that: guidelines. They are not legally enforceable. 2018 edition of "3000" has clause 7.9 to set requirements for EV charging; but since this edition has yet to be cited these 'requirements" are not legally enforceable either. Unless / until ESR 6A is changed, no EV charging ...