Search found 914 matches
- Mon Dec 13, 2021 10:59 am
- Forum: Selection and Installation of Wiring Systems
- Topic: Alterations to cables with green sheathed or bare earths
- Replies: 6
- Views: 5169
Re: Alterations to cables with green sheathed or bare earths
Your interpretation is correct in that it is non-compliant to install bare PECs [5.3.2.4]. Also that 3.8.1 forbids use of green-only to identify PECs by colour - although 5.3.5.3 permits it. And that these rules have an effect on re-routing parts of existing circuits WRT sleeving; 3.8.2 does not pro...
- Fri Dec 10, 2021 12:00 pm
- Forum: Generators and Solar
- Topic: Is stand alone system inspectable
- Replies: 9
- Views: 8898
Re: Is stand alone system inspectable
Yes; ESR 4(2 ) says any definition in Act or ESRs over-rides a definition of same term on a Standard. It can work the other way also, as per ESR 4(3); with terms used in ESRs, but not defined in act or ESRs, carrying definitions from "3000" (for installations) or IEC 60050. Therefore "electrical ins...
- Tue Dec 07, 2021 9:06 am
- Forum: Standards and Legislation
- Topic: Low Risk Work
- Replies: 4
- Views: 3719
Re: Low Risk Work
I think a good general rule is that if you are significantly altering the electrical characteristics of a circuit you are making an alteration rather than maintaining. But like most general rules-of-thumb; it can't be applied strictly. Eg replacing a broken / degraded SERF with another SERF is clear...
- Mon Dec 06, 2021 10:36 am
- Forum: Standards and Legislation
- Topic: Low Risk Work
- Replies: 4
- Views: 3719
Re: Low Risk Work
I agree thus amounts to an alteration of the circuit; and is not maintenance. Also agree that "like-for-like" is not a term that appears anywhere in ESRs, and never has. As a concept it isn't actually very helpful; as it's open to being applied both too strictly and too loosely. When ESRs first came...
- Sat Dec 04, 2021 2:40 pm
- Forum: Electric Vehicles and Charging Systems
- Topic: FSC Origin
- Replies: 4
- Views: 5003
Re: FSC Origin
Ignore my reference to earth monitoring requirement; it's for monitoring the earthing connection to the vehicle.
But I still see no good reason for either the guidelines' requirement for supply from MEN swbd or the '3000" requirement for not-from-outbuilding MEN swbd.
But I still see no good reason for either the guidelines' requirement for supply from MEN swbd or the '3000" requirement for not-from-outbuilding MEN swbd.
- Sat Dec 04, 2021 12:48 pm
- Forum: Electric Vehicles and Charging Systems
- Topic: FSC Origin
- Replies: 4
- Views: 5003
Re: FSC Origin
It's easy enough to work through and so comply with both; at least in theory. the Guideline quoted requires supply from an MEN swbd. There's no definition for this term any more; but can only mean one with an MEN link. In 1993 & 1997 Regs was defined as having both an MEN link and an MEC to an elect...
- Thu Dec 02, 2021 10:38 am
- Forum: Earthing and Bonding
- Topic: PEC Submain
- Replies: 4
- Views: 6969
Re: PEC Submain
Earthing conductors are sized according to the fault current they have to carry; for the short time they have to carry it. That's broadly in proportion to the size of the actives. Clause 5.3.3.1 sets the requirements; and provides 2 methods of determining required size (from Table, or by calculation...
- Tue Nov 30, 2021 2:35 pm
- Forum: Earthing and Bonding
- Topic: 5.7.5 Supplementary Equipotential Bonding
- Replies: 4
- Views: 4687
Re: 5.7.5 Supplementary Equipotential Bonding
Fair point. Even with those words, they don't say "where it has been shown" or "where it is shown", or "if it is shown". It just says "where it can be shown". And since there's no suggestion that any other time applies instead; the correct interpretation of these words is as an explanation of why th...
- Fri Nov 26, 2021 1:22 pm
- Forum: Switchboards
- Topic: Number of Main Switches
- Replies: 22
- Views: 61270
Re: Number of Main Switches
Title of "4777.2" is Grid connection of energy systems via inverters; Part 2 inverter requirements". so hardly surprising that it's focussed on the aspects that relate to connection to grid. 2015 edition does include some info on multi-mode inverters (clause 6); but the first statement is: "unless o...
- Thu Nov 25, 2021 6:15 pm
- Forum: Switchboards
- Topic: Number of Main Switches
- Replies: 22
- Views: 61270
Re: Number of Main Switches
the labelling of main switches is absolutely crucial. "3000"; 7.3.3 requires that any generation system must have an isolating switch at the swbd it is connected to. It also requires no back-feeding; with Exception if network agrees - as for a grid-connected inverter 7.3.4 then adds a number of requ...
- Thu Nov 25, 2021 1:50 pm
- Forum: Switchboards
- Topic: Number of Main Switches
- Replies: 22
- Views: 61270
Re: Number of Main Switches
Perfectly acceptable; as long as they are properly & correctly labelled. For an inverter that only runs as supplementary supply (co-generation; could argue that linking is sensible. But with modern multi-mode inverters that can also act as alternative supply, the last thing you want is linked switches
- Thu Nov 25, 2021 9:56 am
- Forum: Earthing and Bonding
- Topic: 5.7.5 Supplementary Equipotential Bonding
- Replies: 4
- Views: 4687
Re: 5.7.5 Supplementary Equipotential Bonding
You don't need a cure; because there is no problem. What you've got is a case that the Tables don't cover neatly. If you did have a problem; then yes adding a bonding conductor that's essentially in parallel with the PEC is an acceptable method of bringing an excessive EFLI value down to an acceptab...
- Tue Nov 16, 2021 10:31 am
- Forum: Generators and Solar
- Topic: Modules with different azimuth in series
- Replies: 2
- Views: 3805
Re: Modules with different azimuth in series
Agree the citation of later editions would be an improvement.
But until that happens, installations must comply with cited edition.
So the 'let-out" in 2014 edition cannot be used.
It's electrically OK, but legally non-compliant.
And inspection is about certifying both "safe" and 'compliant"
But until that happens, installations must comply with cited edition.
So the 'let-out" in 2014 edition cannot be used.
It's electrically OK, but legally non-compliant.
And inspection is about certifying both "safe" and 'compliant"
- Mon Nov 15, 2021 11:41 am
- Forum: Switchboards
- Topic: First switchboard or metering point.
- Replies: 14
- Views: 10754
Re: First switchboard or metering point.
Maybe. Not sure what the applicable rules for works are, and that option may be restricted. However that's what we'll end up doing if / when TT is introduced; because the installation's earthing system will be separated from the incoming PEN, and the only way to provide fault protection up to & incl...
- Mon Nov 15, 2021 10:12 am
- Forum: Switchboards
- Topic: First switchboard or metering point.
- Replies: 14
- Views: 10754
Re: First switchboard or metering point.
Good question. First would need to establish that it is actually a collection of individual installations; and not a multiple installation. And that means being certain WRT location of the POS(s). Bearing in mind that neither metering nor ICP system for identifying consumers has any direct bearing o...
- Mon Nov 15, 2021 9:47 am
- Forum: Protective Devices
- Topic: AS/NZS 3000:2007 - 3.4.1 A2
- Replies: 16
- Views: 12062
Re: AS/NZS 3000:2007 - 3.4.1 A2
Time was when it could be reasonably assumed that, with a 63A supply fuse, 16 mm2 conductors would be more than adequate for both external & internal sections; and even allow for reasonable future increase in MD But times have changed; and there are a number of factors already in place that mean we ...
- Sun Nov 14, 2021 9:08 am
- Forum: Protective Devices
- Topic: AS/NZS 3000:2007 - 3.4.1 A2
- Replies: 16
- Views: 12062
Re: AS/NZS 3000:2007 - 3.4.1 A2
Agree MD isn't only relevant to cable selection; not to providing the cable with overcurrent protection
- Sun Nov 14, 2021 9:01 am
- Forum: Protective Devices
- Topic: HRC to MCB discrimination
- Replies: 3
- Views: 5128
Re: HRC to MCB discrimination
Correct that only the installation, which starts at the PoS, is required (by ESR59) to comply with "3000". Also consider that while NZ's ESRs require linesco to provide both short circuit and fault protection for mains; they don't have to proved overload protection. And in some States of Oz; they ha...
- Sun Nov 14, 2021 8:41 am
- Forum: Inspection
- Topic: Project Manger Inspecting
- Replies: 4
- Views: 4737
Re: Project Manger Inspecting
ESR 71 refers only to the work that is being inspected; which is the high-risk PEW.
So even if there's only one CoC for the lot, someone who has done only general PEW can inspect the high risk PEW.
So even if there's only one CoC for the lot, someone who has done only general PEW can inspect the high risk PEW.
- Sun Nov 14, 2021 8:37 am
- Forum: Protective Devices
- Topic: AS/NZS 3000:2007 - 3.4.1 A2
- Replies: 16
- Views: 12062
Re: AS/NZS 3000:2007 - 3.4.1 A2
Nearly but not quite. Yes we have to assume BTI; but we don't have to assume "fully surrounded". Adding batt / blanket types of BTI, cables will only end up partially surrounded . So if using Table C5, the CCC will be 63 A. But why use that table, which is based on "worst case", and with fewer optio...
- Fri Nov 12, 2021 8:34 pm
- Forum: Generators and Solar
- Topic: 5033:2012 4.4.1.5 (d) Location of means of isolation for servicing
- Replies: 11
- Views: 8188
Re: 5033:2012 4.4.1.5 (d) Location of means of isolation for servicing
yes, I've never found any "metallic high density PVC" either. And while inserting "or" would have given a choice, i still can't work out how to earth the HDPVC option. So agree it's probably a cock-up; and we have to interpret the intent and hope to not be prosecuted. Actually a compounded cock-up; ...
- Fri Nov 12, 2021 8:26 pm
- Forum: Transportable Installations
- Topic: Transportable Structures supplying power to other structures
- Replies: 10
- Views: 7306
Re: Transportable Structures supplying power to other structures
Cascading is not something I've ever had to deal with directly. Agree it's a mess, compounded by the way ESRs & Standards inter-relate. The possible cross-over between ACS (App K of 3012) and connectable installations is another set of issues. And we also have some 'grey" between whether something i...
- Fri Nov 12, 2021 12:32 pm
- Forum: Transportable Installations
- Topic: Transportable Structures supplying power to other structures
- Replies: 10
- Views: 7306
Re: Transportable Structures supplying power to other structures
Yes this isn't widely understood, so construction sites generally don't comply with 3001 WRT supplies for TSs (both here & in Oz). Agree it's a bit weird to apply full "caravan park" rules, including depth of burial, etc; and may not have been the intent. And will be more so when new requirements fo...
- Fri Nov 12, 2021 8:23 am
- Forum: Selection and Installation of Wiring Systems
- Topic: AS/NZS 3000:2007 - 3.9.4.4 (a)
- Replies: 4
- Views: 3534
Re: AS/NZS 3000:2007 - 3.9.4.4 (a)
Not just un-tradesman-like; it's non-compliant.
- Thu Nov 11, 2021 3:37 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: How to calculate how much volt drop % is already used?
- Replies: 5
- Views: 4934
Re: How to calculate how much volt drop % is already used?
I think not so much that everyone complies;
most give it almost no thought.
But nobody gets caught
most give it almost no thought.
But nobody gets caught
- Thu Nov 11, 2021 10:56 am
- Forum: Transportable Installations
- Topic: Transportable Structures supplying power to other structures
- Replies: 10
- Views: 7306
Re: Transportable Structures supplying power to other structures
Agree Very complex with 2 different standards, plus ESRs. Part of the complexity is that as soon as there are 2 or more sockets on the building site that are intended to supply connectable installations, they become a 'caravan park" (both under Standards, and again under ESRs). Clearly intent of 301...
- Thu Nov 11, 2021 10:47 am
- Forum: Selection and Installation of Wiring Systems
- Topic: How to calculate how much volt drop % is already used?
- Replies: 5
- Views: 4934
Re: How to calculate how much volt drop % is already used?
I am not aware of any easy way to determine the available margin of VD with any sort of accuracy. We can assume % for mains, & for submains, etc, but it can't be anywhere near accurate. And VD is a "must never exceed" limit. I believe it should be a requirement to record, at every switchboard, the s...
- Thu Nov 11, 2021 10:40 am
- Forum: Selection and Installation of Wiring Systems
- Topic: What part is connection? ESR73A
- Replies: 15
- Views: 4220
Re: What part is connection? ESR73A
Both CoC & RoI effectively say "this PEW is OK to be connected to a supply". CoC doesn't say who dod it, just that an identified person is certifying it. RoI also doesn't say who did it, just who certified it and who inspected it. Final connection can then be done by anyone, including by either the ...
- Thu Nov 11, 2021 10:03 am
- Forum: Transportable Installations
- Topic: Transportable Structure Appliance Inlet
- Replies: 8
- Views: 6125
Re: Transportable Structure Appliance Inlet
Discussion with NZ working group for "3001" suggests that while IP X2 is protection against water ingress from any direction, it's about ingress to the inside of the fitting. In this case the pins will have seals, probably O-rings Water on exposed pins not a safety issue because exposed pins can't b...
- Thu Nov 11, 2021 9:58 am
- Forum: Transportable Installations
- Topic: Transportable Structures supplying power to other structures
- Replies: 10
- Views: 7306
Re: Transportable Structures supplying power to other structures
Have raised this with NZ working group for revising "3001".
Initial discussion suggests combination of '3012", "3001" & ESRs means that a straight pass-through set-up is non-compliant
and can't be issued with WoEF.
Initial discussion suggests combination of '3012", "3001" & ESRs means that a straight pass-through set-up is non-compliant
and can't be issued with WoEF.
- Wed Nov 10, 2021 5:57 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: What part is connection? ESR73A
- Replies: 15
- Views: 4220
Re: What part is connection? ESR73A
The Act does allow for connection for purposes of testing Eg you can't test installation of an RCD without connecting some sort of supply. And all required testing must be completed before CoC is issued, else the work hasn't been done 'lawfully & safely". So I am forced to conclude that connecting-f...
- Wed Nov 10, 2021 5:43 pm
- Forum: Transportable Installations
- Topic: Transportable Structure Appliance Inlet
- Replies: 8
- Views: 6125
Re: Transportable Structure Appliance Inlet
yes you could fail for excessive earth resistance readings. Not happy losing my rule-of-thumb; it certainly works for all '3112' sockets that i've found, and wondering how they can claim the IP rating without a cover. maybe the "60309-2" Standard allows for a mated-only rating. And unfortunately App...
- Wed Nov 10, 2021 12:58 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: What part is connection? ESR73A
- Replies: 15
- Views: 4220
Re: What part is connection? ESR73A
Q If I connect and lock out a circuit at switchboard until work has been finished on the circuit have I technically committed an offense? Only compliant method would be to leave the live conductors disconnected until work on circuit is finished A Yes that would be an offence Q What about when you lo...
- Wed Nov 10, 2021 12:49 pm
- Forum: Transportable Installations
- Topic: Transportable Structure Appliance Inlet
- Replies: 8
- Views: 6125
Re: Transportable Structure Appliance Inlet
Interesting
maybe they have seals around each pin, and other measures to prevent ingress; in order to achieve the rating.
In which case my rule-of-thumb isn't entirely valid
And - as you've found - that leaves the possibility of corrosion
maybe they have seals around each pin, and other measures to prevent ingress; in order to achieve the rating.
In which case my rule-of-thumb isn't entirely valid
And - as you've found - that leaves the possibility of corrosion
- Wed Nov 10, 2021 12:40 pm
- Forum: Transportable Installations
- Topic: Transportable Structures supplying power to other structures
- Replies: 10
- Views: 7306
Re: Transportable Structures supplying power to other structures
first part of 2.9 says must comply with '3001 "and' the following which means that all the following are additional to, not instead of ,the provisions of "3001". Exception (B) allows ACS type systems (with pass-through submains) which appears to be there just in case someone decides that an ACS unit...
- Wed Nov 10, 2021 11:41 am
- Forum: Transportable Installations
- Topic: Transportable Structure Appliance Inlet
- Replies: 8
- Views: 6125
Re: Transportable Structure Appliance Inlet
IP24 is a requirement for new inlets as per 3.2.2 If you check the what IP24 means (see App of "3000"); you'll find that IPx4 means protected against water splashed from all directions. That protection can only be attained if there's a cover (applies to both plugs and sockets). Product data sheets w...
- Wed Nov 10, 2021 11:17 am
- Forum: Transportable Installations
- Topic: Woef - Relocatable building permanent connected
- Replies: 1
- Views: 3072
Re: Woef - Relocatable building permanent connected
Directly connected units may appear to be within the definition of 'connectable installation" (Act, modified by ESR 7). However they are clearly NOT within scope of "3001". Nothing requires any connectable installation to ever be issued with a WoEF. Instead, there's a requirement for people intendin...
- Tue Nov 09, 2021 10:26 am
- Forum: Inspection
- Topic: Periodic Assessments for caravan parks
- Replies: 7
- Views: 5836
Re: Periodic Assessments for caravan parks
Most of it is in the words used. Both Regs & Standards are formal documents, that use words in formal ways. So if we take time to read carefully, and leave our pre-conceptions behind, we'll generally be able to arrive at the correct meaning. We need to consider why particular words have been used; c...
- Tue Nov 09, 2021 9:12 am
- Forum: Selection and Installation of Wiring Systems
- Topic: What part is connection? ESR73A
- Replies: 15
- Views: 4220
Re: What part is connection? ESR73A
Simply avoiding doing the connection won't fully absolve you. We all carry responsibility for safety & compliance of the PEW we do. Issuing a CoC is the formal declaration & acceptance of this. On many jobs there will have been more than one person doing PEW, but often only one issues a single CoC t...
- Mon Nov 08, 2021 4:58 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: What part is connection? ESR73A
- Replies: 15
- Views: 4220
Re: What part is connection? ESR73A
ESRs make connection to a supply of electricity the key issue for responsibility / liability. It's the person (about to connect who is required to ensure that CoC(s) & RoI(s) have been issued, and for pre-connection checks in addition. And then, after connection, they issue the ESC. which is why ESR...
- Mon Nov 08, 2021 10:50 am
- Forum: Selection and Installation of Wiring Systems
- Topic: What part is connection? ESR73A
- Replies: 15
- Views: 4220
Re: What part is connection? ESR73A
Exactly. The key thing in this clarification is that "connection" is PEW. Operating a switch isn't PEW, so can't be 'connection. Same for inserting a fuse carrier. If you make carry out PEW such that someone else can energise without any further PEW, you've connected. That includes connecting a neut...
- Mon Nov 08, 2021 10:44 am
- Forum: Inspection
- Topic: Boat eWOF with incorrect polarity on GPO's
- Replies: 1
- Views: 2989
Re: Boat eWOF with incorrect polarity on GPO's
The use of travel adaptors is not generally a good idea, as some of them are electrically unsafe. However there is NO requirement to change sockets for issue of a WoEF for use of a boat's connectable installation in NZ. GPOs on boats that have been imported, and in which NZ appliances are intended t...
- Mon Nov 08, 2021 9:48 am
- Forum: Inspection
- Topic: Periodic Assessments for caravan parks
- Replies: 7
- Views: 5836
Re: Periodic Assessments for caravan parks
Yes, there's a difference between sockets intended for supply to connectable installations, and general purpose sockets. Covered by 2 different clauses, C5.3 for the CI sockets, and C5.4 for GPOs GPOs will typically be "3112" type, rated 10 A - but could be any type and any rating. And yes the bench...
- Sun Nov 07, 2021 2:56 pm
- Forum: Inspection
- Topic: Periodic Assessments for caravan parks
- Replies: 7
- Views: 5836
Re: Periodic Assessments for caravan parks
Yes, PA must be i.a.w the relevant Standard; which sets the benchmarks against which the installation is assessed. For a caravan park; the benchmarks are in App C of '3001. Yes, any aspect that falls short of the applicable benchmark should be noted in the RoA which must be issued regardless of whet...
- Sat Nov 06, 2021 12:47 pm
- Forum: Inspection
- Topic: Periodic Assessments for caravan parks
- Replies: 7
- Views: 5836
Re: Periodic Assessments for caravan parks
Periodic Assessment is not like certification & inspection of PEW. With certification / inspection, there's a set of criteria that the (new) PEW mist comply with. That makes it a "pass vs fail" exercise. Issuing a WoEF is similar. In order for a valid WoEF to be issued, the caravan (or whatever) mus...
- Fri Nov 05, 2021 4:47 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: Does 3.4.3 apply to earths?
- Replies: 4
- Views: 2704
Re: Does 3.4.3 apply to earths?
Like the rest of 3.4; 3.4.3 is about CCC, and this applies for load-carrying conductors. So 3.4 refers to CCCs as per 3008.1 series for load-carrying The CCC ratings are maximum constant currents under a variety of installation conditions It doesn't apply directly to PECs, because they don't carry l...
- Fri Nov 05, 2021 2:40 pm
- Forum: Distribution, Networks & Metering
- Topic: Private network
- Replies: 5
- Views: 5222
Re: Private network
Unsure as to any particular advantage in context of normal distribution. Just something that happens in some multi-occupancy properties. And for subdivisions, the developer may have installed the distribution, but maybe the local electricity distributor declines to accept ownership (and ongoing resp...
- Thu Nov 04, 2021 12:32 pm
- Forum: Transportable Installations
- Topic: Non-relocatable building
- Replies: 4
- Views: 4491
Re: Non-relocatable building
I'm sure that if the structure is fixed to the ground, ESR 60 does not require compliance with "3001". Also that as a non-caravan park, the socket is also not required to comply with "3001"; but it does of course have to comply with '3000" Next question is whether supply via detachable connection ( ...
- Thu Nov 04, 2021 12:01 pm
- Forum: Distribution, Networks & Metering
- Topic: Private network
- Replies: 5
- Views: 5222
Re: Private network
Agree that any "main earthing system" that is installed within an installation is high risk PEW and must be inspected. Same for installation of "mains". It's important that: - only PEW on an "installation" needs to be certified; - only PEW on an "installation" has a risk classification under ESR 6A;...
- Thu Nov 04, 2021 9:44 am
- Forum: Transportable Installations
- Topic: Non-relocatable building
- Replies: 4
- Views: 4491
Re: Non-relocatable building
We can also look to what "3001" says about scope; eg that it excludes "Transportable structures, such as homes, huts, construction sheds and tents that are fixed in position." But that's putting the cart before the horse; because a Standard only gets its authority from the way it's cited (or not) in...