- Mon Sep 27, 2021 6:53 pm
- Forum: Standards and Legislation
- Topic: Proposed limits of work
- Replies: 5
- Views: 4015
Re: Proposed limits of work
we could also co-ordinate the submissions, that way the EWRB get a clear picture of what electrical workers want/think
- Mon Sep 27, 2021 5:07 pm
- Forum: Standards and Legislation
- Topic: Proposed limits of work
- Replies: 5
- Views: 4015
Re: Proposed limits of work
do a submission, that's what the email is about, I see the point about EST's replacing a mains entry box, technically it is low risk, but keep in mind poor wording in the past means that a lineman can issue a COV for an installation.......
- Wed Sep 15, 2021 5:01 pm
- Forum: Protective Devices
- Topic: Fuses in parallel
- Replies: 5
- Views: 5551
Re: Fuses in parallel
The cables are not individually protected, the load side of the fuse holders at the network end are bus tied together, at the main switch installation the cables are directly bolted to the live side of the main switch. the set up effectively 2 parallel fuses(per phase) mechanically linked together s...
- Tue Sep 14, 2021 5:36 pm
- Forum: Protective Devices
- Topic: Fuses in parallel
- Replies: 5
- Views: 5551
Fuses in parallel
So a bit of a technical question, Keep in mind this is in a WORKS environment not an installation. Network electrical engineer (I use the word engineer loosely here as it's a job title and the person may or may not be an electrical engineer - I don't know) has specified a service fuse to a new facto...
- Sat Aug 28, 2021 9:42 am
- Forum: Selection and Installation of Wiring Systems
- Topic: Ring circuits - Are they a complaint method?
- Replies: 2
- Views: 2130
Re: Ring circuits - Are they a complaint method?
I'm not sure of the legality of ring circuits, but as they are generally not the way things are done in NZ and almost every electrician in NZ could easily be caught out if they came across one. I came across one many years ago, a fellow employee done a sub board change in a commercial installation n...
- Sun May 30, 2021 7:10 pm
- Forum: Appliances
- Topic: Scope of Testing as applicable to personal items
- Replies: 2
- Views: 4189
Re: Scope of Testing as applicable to personal items
3760 isn't a cited standard, so there is no mandated rule to do testing and tagging, but the ESR's say that if an appliance is tested to 3760 (and passes) then it is deemed "Electrically Safe" this meets worksafes requirements of "Taking reasonable actions" in relation to safety of electrical applia...
- Wed May 12, 2021 4:51 pm
- Forum: Distribution, Networks & Metering
- Topic: Connection at pole/plinth fuse
- Replies: 8
- Views: 8249
Re: Connection at pole/plinth fuse
Typically in the past network companies had their own inspectors who would do this kind of work, this has kind of followed through to today's work, except that most network companies authorize a contractor who has an inspector on staff to do this. While most this work could be done by a line worker,...
- Wed Apr 28, 2021 5:02 pm
- Forum: Standards and Legislation
- Topic: Certified Designs - ESR58
- Replies: 7
- Views: 3382
Re: Certified Designs - ESR58
the way I read it:-
Part 1 must be to a CD
Part 2 can be to a CD but does not have to be.
Part 1 must be to a CD
Part 2 can be to a CD but does not have to be.
- Fri Apr 23, 2021 2:21 pm
- Forum: Standards and Legislation
- Topic: MBIE looking at updating ESR
- Replies: 2
- Views: 1815
Re: MBIE looking at updating ESR
I've put my submission in.
- Tue Apr 20, 2021 6:01 am
- Forum: Testing & Verification
- Topic: Certified Design?
- Replies: 4
- Views: 5298
Re: Certified Design?
the food tray sealer is an appliance, not part of the installation. No certified design needed. An ESC would be required to confirm it's electrical safety
- Sun Apr 18, 2021 8:42 pm
- Forum: Testing & Verification
- Topic: Motor Circuit Breaker Earth Continuity
- Replies: 3
- Views: 4552
Re: Motor Circuit Breaker Earth Continuity
I'll start this with...."Correct me if i'm wrong" There are a lot more things to consider on a motor circuit breaker compared to a regular circuit breaker. Some have adjustable trip time setting (some don't). So the way I understand it should work is, if the circuit is for personal protection then t...
- Sun Apr 18, 2021 9:19 am
- Forum: Inspection
- Topic: Private network
- Replies: 11
- Views: 12977
Re: Private network
This wouldn't come in to play in this instance as you said it was going to serve a private network of several hundred dwellings, part ob (b) (i)."..... and not for supply to any other person" which is for one dwelling only
- Fri Apr 16, 2021 5:37 pm
- Forum: Inspection
- Topic: Private network
- Replies: 11
- Views: 12977
Re: Private network
Yes, I don't know of anything that exempts a private network
All high risk work needs to be logged on the high risk database private network or not
All high risk work needs to be logged on the high risk database private network or not
- Sun Apr 11, 2021 6:44 pm
- Forum: Damp Situations
- Topic: power points under eves
- Replies: 6
- Views: 7084
Re: power points under eves
You can only account for "normal" conditions, pretty much any socket, IP53 or IP56 isn't going to standup to been water blasted.
- Fri Mar 19, 2021 5:12 pm
- Forum: Welcome to the NZ's Electrical Forum
- Topic: Becoming an iqp for emergency lighting
- Replies: 3
- Views: 7899
Re: Becoming an iqp for emergency lighting
I done it for both Auckland and Hamilton, there were a few hoops to jump thru for Hamilton not too hard to achieve, For Auckland was a real mission, ended up going on the IQP course, had to demonstrate that I had all the forms and paperwork set up, it took multiple attempts as the attitude was taken...
- Sat Mar 13, 2021 3:22 pm
- Forum: General Electrical Discussions
- Topic: Building Inspector quoting from AS/NZS 3000:2018
- Replies: 7
- Views: 6477
Re: Building Inspector quoting from AS/NZS 3000:2018
Time for a sit down with the head contractor to nut out where everyone's responsibilities lie. If the building inspector is making things difficult, it is the head contractors problem to sort, you just need to make it clear to the head contractor (in a friendly way) that your CoC/ESC is what the bui...
- Fri Mar 12, 2021 4:47 pm
- Forum: General Electrical Discussions
- Topic: Building Inspector quoting from AS/NZS 3000:2018
- Replies: 7
- Views: 6477
Re: Building Inspector quoting from AS/NZS 3000:2018
What Alec has said pretty much sums it up. Personally I would have told the building inspector that he is required by law to accept the ESC/CoC, if he wants to start telling the electrician how they should be doing their work he better ensure he has the qualification and practicing license to back i...
- Wed Feb 24, 2021 6:33 pm
- Forum: Generators and Solar
- Topic: US enphase inverters
- Replies: 2
- Views: 3343
Re: US enphase inverters
Part 1 installations *must* be a certified design, Part 2 installations can be a certified design but don't have to be. Sounds like a bit of a can of worms here, It would be a good idea to insist on a certified design so it very clear what is been done and why and how compliance is going to be achie...
- Fri Feb 19, 2021 6:19 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: Overhead Submain Cabling
- Replies: 17
- Views: 7807
Re: Overhead Submain Cabling
Hi @DougP, I do work for a line company, and yes the service connections and the insulation falling apart is a BIG problem, we don't sleeve the PVC, we join UV stable cable on to the end and heavy wall heatshrink the link and the service PVC, this also has the advantage of creating a water barrier t...
- Wed Jan 27, 2021 5:41 pm
- Forum: Selection and Installation of Wiring Systems
- Topic: Heat pump , max demand calc
- Replies: 6
- Views: 3747
Re: Heat pump , max demand calc
I would be leaning towards the max amps, there is no way you can determine the usage of the heat pump, a safe assumption would to use the max amps.
- Fri Dec 25, 2020 11:50 am
- Forum: Earthing and Bonding
- Topic: While you're waiting for your Christmas roast to cook..
- Replies: 4
- Views: 4094
Re: While you're waiting for your Christmas roast to cook..
Possibly What's the issue you have? I guess you'd have to be careful of parallel E/N paths as always but I can't see why you couldn't off the top of my head Greg where do you get the notion of every submain needing a PEC in 2018? 5.5.3.1 (c) still allows the use of a PEN submain does it not? I stan...
- Fri Dec 25, 2020 11:28 am
- Forum: Earthing and Bonding
- Topic: While you're waiting for your Christmas roast to cook..
- Replies: 4
- Views: 4094
Re: While you're waiting for your Christmas roast to cook..
Yes, doesn't matter what the submain is for. But for the sake of making things easy run an PEC, means no MEN link, earth electrode or inspection (yeah I know the old chestnut of inspection of sub board MEN's/earthing).
Although not cited yet in NZ AS/NZS 3000:2018 requires all submains to have a PEC.
Although not cited yet in NZ AS/NZS 3000:2018 requires all submains to have a PEC.
- Sat Dec 19, 2020 8:52 pm
- Forum: Apprentices and training
- Topic: is it ok for apprentices to work alone?
- Replies: 6
- Views: 11795
Re: is it ok for apprentices to work alone?
The EWRB publish a guide line for trainee supervision.
https://www.ewrb.govt.nz/assets/documen ... ficate.pdf
https://www.ewrb.govt.nz/assets/documen ... ficate.pdf
- Mon Dec 14, 2020 5:50 am
- Forum: Protective Devices
- Topic: Range Socket Outlet Addition - RCD?
- Replies: 2
- Views: 4030
Re: Range Socket Outlet Addition - RCD?
additional sockets are required to be protected at the source, doesn't matter what the source is.
- Sun Dec 13, 2020 9:12 pm
- Forum: Standards and Legislation
- Topic: AS/NZS 3000:2007 Superseded?
- Replies: 9
- Views: 4616
Re: AS/NZS 3000:2007 Superseded?
2018 is the newest version, but the ESR's cite the 2007 Version, it's good practice to use the 2018 version but there are a few instances where 2018 contradicts 2007, in those cases 2007 should be used.
- Fri Dec 11, 2020 5:36 pm
- Forum: Off Topic
- Topic: Tell everyone your funny story
- Replies: 3
- Views: 8400
Tell everyone your funny story
Just for something a bit different, tell everyone a funny story that happened to you or a workmate, Just so we don't get in trouble - no people or company names. I'll start... A few years back, 1st thing in the morning completing our paperwork from the day before, making a coffee in the break room a...
- Thu Dec 03, 2020 5:50 am
- Forum: Switchboards
- Topic: Main switch upgrade
- Replies: 12
- Views: 9921
Re: Main switch upgrade
Interesting I thought it was more needed to see if the existing mains CCC is fit for the new increases capacity and if the EFLI is low enough to operate new short circuit protection with in 5s etc But maybe that obviously has to be done but its more responsible of person actually putting in the new...
- Wed Dec 02, 2020 8:35 pm
- Forum: General Electrical Discussions
- Topic: Electric Fence/induced voltage
- Replies: 3
- Views: 4621
Re: Electric Fence/induced voltage
Remember this is not a dairy farm, it's a bull farm and they are very stroppy that's why they have a electric fence that packs a wallop IR tests are great, it's definitely induced, it's been that way since the day it was laid in the ground and before it ever was connected. As far as earths for the e...
- Wed Dec 02, 2020 5:19 pm
- Forum: Inspection
- Topic: When do COC/ROI/ESC become active
- Replies: 2
- Views: 4305
Re: When do COC/ROI/ESC become active
Personally if it's a fail then you should be keeping the ROI, It may just one day save you.
As far as when the COC/ROI/ESC becomes active, very good question, I would say once dated and signed.
As far as when the COC/ROI/ESC becomes active, very good question, I would say once dated and signed.
- Wed Dec 02, 2020 4:43 pm
- Forum: General Electrical Discussions
- Topic: Electric Fence/induced voltage
- Replies: 3
- Views: 4621
Electric Fence/induced voltage
We have a installation in a rural area. A new shed has been built around 400m from the point of supply. The mains are 240AL tailed down to 16CU at each end. During installation BEFORE any connection to the network the guys doing the jointing between the CU and AL were getting shocks from the cable, ...
- Sat Nov 21, 2020 11:55 am
- Forum: Distribution, Networks & Metering
- Topic: Connection at pole/plinth fuse
- Replies: 8
- Views: 8249
Re: Connection at pole/plinth fuse
As an electrician you have a duty of care to leave it in a safe condition, as normally you would not be allowed access to the service fuse - Ring the network company, Personally if it was me and I could reasonably access the service fuse without damaging the pillar I would remove the fuse and advise...
- Sun Nov 15, 2020 8:04 pm
- Forum: Inspection
- Topic: WoEF
- Replies: 6
- Views: 5922
Re: WoEF
I don't think a WOEF is classed as an inspection, but it must be done by a person who is authorised to inspect mains work ESR 78 (1) (a).
as far as been PEW, yes., ESR 65 (6) tells us certification (which is what a WOEF is?) is PEW, but does not require a COC.
as far as been PEW, yes., ESR 65 (6) tells us certification (which is what a WOEF is?) is PEW, but does not require a COC.
- Wed Nov 11, 2020 4:33 pm
- Forum: Earthing and Bonding
- Topic: Cable tray
- Replies: 5
- Views: 4453
Re: Cable tray
What it comes down to is installing to the conditions, we all know that things like cable tray and switchboards are targets for forklift drivers and it's just a matter of time before they get hit. I have in the past insisted on bollards (which are also a target for the forklift drive) which have pro...
- Wed Nov 11, 2020 5:34 am
- Forum: Earthing and Bonding
- Topic: Cable tray
- Replies: 5
- Views: 4453
Re: Cable tray
for double insulated conductors no, but for good practice yes, the photo is a good example
- Wed Oct 28, 2020 9:04 pm
- Forum: Inspection
- Topic: Esr 70
- Replies: 7
- Views: 6660
Re: Esr 70
Yes the inspector is responsible, there have been a number of polarity reversals on mains in the past and inspectors prosecuted for it. Polarity checks are a mandatory check and it was obvious that these were not done. So check whatever you need to be happy, don't be afraid to fail the inspection if...
- Wed Oct 28, 2020 8:12 pm
- Forum: Inspection
- Topic: Esr 70
- Replies: 7
- Views: 6660
Re: Esr 70
There is an element of trust between the inspector and electrician, as an inspector how you achieve the inspection is up to you, personally if it's for someone you don't know then poke your head thru the manhole and have a look, as the electrician to dig a hole where the mains were buried and measur...
- Sat Oct 24, 2020 9:46 am
- Forum: Distribution, Networks & Metering
- Topic: Connection to Pole Top Fuses.
- Replies: 3
- Views: 4746
Re: Connection to Pole Top Fuses.
Re-reading your original post, A couple of things, usually the demarcation point for works vs. installation is the boundary line, but it is common for this line to be inside the boundary on a private pole at the pole fuses if the power company has an easement. on the application for the BTS, did it ...
- Thu Oct 22, 2020 5:11 pm
- Forum: Distribution, Networks & Metering
- Topic: Connection to Pole Top Fuses.
- Replies: 3
- Views: 4746
Re: Connection to Pole Top Fuses.
As it's a private pole anyone with the suitable qualification and is competent can do this, and Electrical Inspector, Electrician, Distribution Line mechanic. - Technically an Electrical Engineer could but doubt they would be competent or even want to. Ask the lines contractor why an Electrician can...
- Sat Oct 17, 2020 12:06 pm
- Forum: Generators and Solar
- Topic: Lockable main switch at switchboard connection - 4777.1 2005
- Replies: 7
- Views: 4819
Re: Lockable main switch at switchboard connection - 4777.1 2005
the way I read it, is the switch between the output of the inverter and the switchboard it connects to, the switch doesn't have to be in the switchboard, it could be beside, above or below, or at the inverter.
- Tue Oct 13, 2020 3:58 pm
- Forum: Appliances
- Topic: Is a rocker switch able to installed horizontally?
- Replies: 5
- Views: 5007
Re: Is a rocker switch able to installed horizontally?
As an alternative, the contactor could be installed in an enclosure in the ceiling space above the kitchen. Or in a corner of a kitchen cupboard, depending on the physical size of the contactor you may even be able to squeeze it in to the flush box.
- Tue Oct 13, 2020 5:44 am
- Forum: Appliances
- Topic: Is a rocker switch able to installed horizontally?
- Replies: 5
- Views: 5007
Re: Is a rocker switch able to installed horizontally?
the alternative is to install a contactor in the switchboard and have a control switch mounted in the position you want for the oven
- Sun Oct 11, 2020 7:38 pm
- Forum: Inspection
- Topic: Medical
- Replies: 4
- Views: 4061
Re: Medical
I've done a little bit of BPA and CPA work at Waikato Hospital, while I don't know everything about the areas feel free to bounce some questions off me
- Sun Oct 11, 2020 5:28 pm
- Forum: Inspection
- Topic: Medical
- Replies: 4
- Views: 4061
Re: Medical
You should find that the BPA and CPA should be marked on the floor with inlays in the flooring.
But the answer to Q1and Q2 is yes.
BPA and CPA can quite hard to wrap your head around and get it right.
But the answer to Q1and Q2 is yes.
BPA and CPA can quite hard to wrap your head around and get it right.
- Fri Oct 02, 2020 5:48 am
- Forum: Distribution, Networks & Metering
- Topic: Connection at pole/plinth fuse
- Replies: 8
- Views: 8249
Re: Connection at pole/plinth fuse
Generally the network company arranges connection at the pole/plinth, it could be their network connection team it could be subcontracted out to another company, basically the pole/plinth belongs to the network company so they says who does the connection there
- Wed Sep 30, 2020 6:04 am
- Forum: Generators and Solar
- Topic: Earth wire type for PV Array
- Replies: 17
- Views: 6113
- Wed Sep 23, 2020 5:52 pm
- Forum: Earthing and Bonding
- Topic: Testing for presence of a main earth when one can't be found
- Replies: 12
- Views: 13530
Re: Testing for presence of a main earth when one can't be found
Main earths in older buildings can be difficult to find, a couple of examples - under a deck that was added at a later date only found it we I looked a little harder. another one, concreted poured over and around it - only found it as we were doing a OHUG and had to cut the concrete for the new main...
- Mon Sep 14, 2020 7:30 am
- Forum: Generators and Solar
- Topic: Connection of PV exposed conductive parts
- Replies: 5
- Views: 2857
Re: Connection of PV exposed conductive parts
Just to make things a little clearer, what standard are you referring to?
- Sun Sep 13, 2020 8:18 am
- Forum: Electric Vehicles and Charging Systems
- Topic: EV charger isolator location.
- Replies: 1
- Views: 4176
Re: EV charger isolator location.
IMO, the most important word is "GUIDELINES" the is no compulsion to follow these (yet). But common sense and in the event of an issue they would be best practice to follow. If it was me I would have an isolator in proximity to the charger or make a reccomendation that in order to comply with the gu...
- Fri Sep 11, 2020 5:48 pm
- Forum: Protective Devices
- Topic: Deleted post can't find? Is descrimination of same branch required
- Replies: 3
- Views: 4720
Re: Deleted post can't find? Is descrimination of same branch required
There was an SQL update by the web provider that broke the server, they ended up doing a rollback and the end result was some posts been lost.
- Wed Sep 09, 2020 5:42 pm
- Forum: Announcements
- Topic: Forums down earlier today
- Replies: 1
- Views: 4701
Forums down earlier today
Thanks to all those that emailed me to let me know that there was an issue. It has been resolved with no loss of data. And for those that want to know what happened. My web space provided upgraded the SQL database for another one of their customers last night, lets just say it didn't go to well and ...