Search found 478 matches

by JamieP
Wed Aug 10, 2022 5:32 pm
Forum: Selection and Installation of Wiring Systems
Topic: Installation of cable with green earth
Replies: 4
Views: 4517

Re: Installation of cable with green earth

I guess I just wasn't sure if there was any difference between the cable never being installed vs an alteration to one that was existing Was unsure if it had to meet current standards being installed for the first time whereas I thought ESR113 would apply if it had already been installed before but ...
by JamieP
Tue Aug 09, 2022 12:02 pm
Forum: Selection and Installation of Wiring Systems
Topic: Installation of cable with green earth
Replies: 4
Views: 4517

Installation of cable with green earth

Customer has supplied old cable to use that is in good condition except that it has a plain green earth.

Can I use this is I sleeve or shrink the earth green/yellow at terminations?
by JamieP
Thu Aug 04, 2022 12:56 pm
Forum: Selection and Installation of Wiring Systems
Topic: Max Demand for Connectable Installations
Replies: 4
Views: 4268

Re: Max Demand for Connectable Installations

I was under the impression App A was for caravan parks etcetc

I am simply doing a supply to a shed and putting a single connection point

Agree though, allowing the full 16A seems to be the best option
by JamieP
Thu Aug 04, 2022 12:53 pm
Forum: Earthing and Bonding
Topic: Do I need to provide certification if I only install earths?
Replies: 7
Views: 6097

Re: Do I need to provide certification if I only install earths?

Appreciate the input and opinions, I agree, rather play it safe than not
by JamieP
Mon Aug 01, 2022 4:09 pm
Forum: Selection and Installation of Wiring Systems
Topic: Max Demand for Connectable Installations
Replies: 4
Views: 4268

Max Demand for Connectable Installations

I am doing max demand calculations for a shed and there is to be a 16A socket outlet set up in accordance with 3001 but I'm just wondering what value I use for max demand? B ii and b iii don't explicitly apply Possibly M? But what can I assess? Or because the connectable is current limited by a 16A ...
by JamieP
Wed Jul 20, 2022 7:35 pm
Forum: Earthing and Bonding
Topic: Do I need to provide certification if I only install earths?
Replies: 7
Views: 6097

Re: Do I need to provide certification if I only install earths?

I'm not really sure to be honest. They aren't inside any zone but I guess they are directly associated with the hazardous area. Thanks Greg, I'm currently looking into this myself but just wanted to external opinions.
by JamieP
Wed Jul 20, 2022 3:20 pm
Forum: Earthing and Bonding
Topic: Do I need to provide certification if I only install earths?
Replies: 7
Views: 6097

Do I need to provide certification if I only install earths?

My situation is I have been asked to install some equipotential bonds between pipes that carry explosive dust. The inside of the pipes is Z20. Outside the pipes is unzoned. The incoming pipe gets swapped between 2 different outgoing options via a flexible coupling so th the two equipotential bonds e...
by JamieP
Sun Jun 26, 2022 5:47 pm
Forum: Standards and Legislation
Topic: Mains switches
Replies: 3
Views: 3757

Re: Mains switches

Oh yeah, I see the term Main Switchgear now Interesting It just got me thinking in regards to how today's rules can be applied to existing installation in regards to different terms used for things over the years, mainly in regards to people discussing things such as "main switch" heights on old swi...
by JamieP
Thu Jun 23, 2022 1:02 pm
Forum: Switchboards
Topic: 0.6m access for domestic switchboards?
Replies: 2
Views: 3462

Re: 0.6m access for domestic switchboards?

Thank you Alec
by JamieP
Tue Jun 21, 2022 8:03 pm
Forum: Standards and Legislation
Topic: Mains switches
Replies: 3
Views: 3757

Mains switches

Quite interesting that I've just had a look through but the term main switch only seem to have been a thing once 3000 arrived I can't find much in past Regulations but just curious if the term main switch was used in the industry prior to this or if people referred to the incoming isolation switch a...
by JamieP
Tue Jun 21, 2022 7:55 pm
Forum: Switchboards
Topic: 0.6m access for domestic switchboards?
Replies: 2
Views: 3462

0.6m access for domestic switchboards?

Does 2.9.2.2 (I) apply to domestic switchboards? I understand the exception "Exception: The requirements for doors of switchrooms and for emergency exit facilities need not apply to single domestic electrical installations." But it's a bit unclear which parts this does and doesn't cover to me. Altho...
by JamieP
Mon Jun 20, 2022 10:53 am
Forum: Testing & Verification
Topic: RCD testing - to test? Or not to test? as per ESR24
Replies: 4
Views: 4375

Re: RCD testing - to test? Or not to test? as per ESR24

Thank you once again Alec, appreciated
by JamieP
Sat Jun 18, 2022 1:55 pm
Forum: Testing & Verification
Topic: RCD testing - to test? Or not to test? as per ESR24
Replies: 4
Views: 4375

Re: RCD testing - to test? Or not to test? as per ESR24

It was just the 63 (1) "All prescribed electrical work done on a low or extra-low voltage installation or part installation must be tested" (b) "to ensure that the installation or part installation is not electrically unsafe" Which was required as well as the other items in 63 (1) It just made me wo...
by JamieP
Fri Jun 17, 2022 11:45 am
Forum: Testing & Verification
Topic: RCD testing - to test? Or not to test? as per ESR24
Replies: 4
Views: 4375

RCD testing - to test? Or not to test? as per ESR24

Now, been covered before but hopefully someone can word things better for me in regards to this To put simply, I agree ESR24 has nothing to do with testing. ESR63 covers testing and we test as per 3000. Push button test or a specific device but the outcome is to ensure all poles disconnect. However ...
by JamieP
Fri Jun 03, 2022 2:00 pm
Forum: Selection and Installation of Wiring Systems
Topic: Black as an active? Table 3.4
Replies: 2
Views: 3447

Re: Black as an active? Table 3.4

I guess what's confused me a bit is 3.8.3.3 it seems to show the correlation between the colours which I understand but I couldn't see where it actually said these colors are acceptable but I'd missed 3.8.3.2 (b) which is where it allows flexible cords or cables to use the European colours for insta...
by JamieP
Thu Jun 02, 2022 7:34 pm
Forum: Selection and Installation of Wiring Systems
Topic: Black as an active? Table 3.4
Replies: 2
Views: 3447

Black as an active? Table 3.4

I understand European colours are discussed in 3000 and it's common to have a black as L2 but is the use of European multiphase non-compliant as installation wiring due to table 3.4 only allowing colours other than those listed and this list includes black

Curious if I'm missing something or not
by JamieP
Tue May 31, 2022 8:53 am
Forum: Appliances
Topic: Motor - Low insulation resistance
Replies: 6
Views: 5923

Re: Motor - Low insulation resistance

Couldn't tell you sorry, I declined to connect and made them swap it out. I felt happiest this way but it just got me thinking where others draw the line with these things because as you say, I have heard of low readings disappeared once run and dried out or similar

Thanks for the input mate
by JamieP
Mon May 30, 2022 7:19 pm
Forum: General Electrical Discussions
Topic: Bootlace Crimpers - Hex vs Square
Replies: 3
Views: 4634

Re: Bootlace Crimpers - Hex vs Square

Cheers mate

I ended up getting and absolutely love my Weidmuller PZ6 ROTO LS

0.14-6mm singles and 0.14-4mm doubles

They use a trapezoid crimp
by JamieP
Mon May 30, 2022 10:54 am
Forum: Standards and Legislation
Topic: How to deal with conflicts?
Replies: 1
Views: 2326

How to deal with conflicts?

4777 gets talked about a lot. We all know that 4777.1:2005 is cited, with 4777.1:2016 seemingly having much better information. Now I understand the whole best thing is to work to the most up to date guidance provided you don't contradict the cited version. I don't know 100% but let's just say that ...
by JamieP
Mon May 23, 2022 7:25 pm
Forum: Selection and Installation of Wiring Systems
Topic: 4.7.1 Does a remote contactor with a local control switch meet the requirements?
Replies: 7
Views: 5326

Re: 4.7.1 Does a remote contactor with a local control switch meet the requirements?

More directed that it seemed to want the switch to switch all actives locally, not to switch all actives remotely

But what you say makes sense, appreciated
by JamieP
Sun May 22, 2022 6:59 pm
Forum: Selection and Installation of Wiring Systems
Topic: 4.7.1 Does a remote contactor with a local control switch meet the requirements?
Replies: 7
Views: 5326

Re: 4.7.1 Does a remote contactor with a local control switch meet the requirements?

Neither arrangement does

But neither arrangement has too because a device for isolation is not required. Only a switch.

Unless you're referring to the contactor at the switchboard? That will still have a protective device upstream of it.
by JamieP
Sun May 22, 2022 5:51 pm
Forum: Selection and Installation of Wiring Systems
Topic: 4.7.1 Does a remote contactor with a local control switch meet the requirements?
Replies: 7
Views: 5326

4.7.1 Does a remote contactor with a local control switch meet the requirements?

"shall be provided with a switch, operating in all active conductors, mounted near the appliance in a visible and readily accessible position." Reading this the switch that is mounted near the appliance in a visible and readily accessable position must operate in all active conductors but a local co...
by JamieP
Sat May 21, 2022 1:30 pm
Forum: Selection and Installation of Wiring Systems
Topic: Installation of conduits and ducts - is this PEW?
Replies: 4
Views: 3213

Re: Installation of conduits and ducts - is this PEW?

Of course. My question was more around compliance of my wiring but I guess as you've indicated above unless I can prove it meets the requirements of today's rules to be suitable for my additional cables then I shouldn't be using it because I can't garentee it complies so my options are either prove ...
by JamieP
Fri May 20, 2022 7:06 pm
Forum: Selection and Installation of Wiring Systems
Topic: Installation of conduits and ducts - is this PEW?
Replies: 4
Views: 3213

Re: Installation of conduits and ducts - is this PEW?

Further question: Situations where there are existing ducts/conduits with existing cables Would this be the same case that to run additional cables in them we would have to ensure they were up to current standards so our cables can be certified as compliant? Or could we treat it like a complied when...
by JamieP
Fri May 20, 2022 2:36 pm
Forum: Selection and Installation of Wiring Systems
Topic: Installation of conduits and ducts - is this PEW?
Replies: 4
Views: 3213

Installation of conduits and ducts - is this PEW?

Quite frequently the installation of ducts and conduits underground is outsourced with no way to know if it's been done correctly unless being there at the time or digging it up to check. I'm just curious if it would be PEW or require a license/registration to do so? Should a CoC be issued? In most ...
by JamieP
Sun May 15, 2022 10:28 am
Forum: Damp Situations
Topic: Sink zones
Replies: 7
Views: 7975

Re: Sink zones

I believe this has come up a few times and Alec said that the pictures were incorrect. I believe it's like the usual string theory he mentions and should be rounded like you've indicated. 6.2.2.2 the actual clause that gives the measurements rather than the informative pictures to me indicates a 150...
by JamieP
Thu May 05, 2022 11:00 am
Forum: Transportable Installations
Topic: Evading EWOFs
Replies: 3
Views: 3883

Re: Evading EWOFs

So in terms of compliance, to put responsibility off me and back to them, either need a EWoF if classed as a transportable but if not transportable they need to supply me with a CoC being part of the installation?
by JamieP
Wed May 04, 2022 5:34 pm
Forum: Transportable Installations
Topic: Evading EWOFs
Replies: 3
Views: 3883

Evading EWOFs

I have been supplied a bunch of buildings that are essentially transportable installation. However the buildings have shown up with a mains entry box. I believe they are changing them from a plug in connection to get around the technicality of being a trainsportable by making them direct connected. ...
by JamieP
Mon May 02, 2022 7:15 pm
Forum: Earthing and Bonding
Topic: MEC sized by max demand
Replies: 7
Views: 8998

Re: MEC sized by max demand

I'd say yes, the point is that the limiting factor is based on volt drop considerations not CCC so I don't know how that would be any different
by JamieP
Sat Apr 30, 2022 3:16 pm
Forum: Appliances
Topic: Motor - Low insulation resistance
Replies: 6
Views: 5923

Re: Motor - Low insulation resistance

This wouldn't be within the scope of 3760 though, would it?

Or are you just applying that as a closest available guide to this situation
by JamieP
Fri Apr 29, 2022 5:42 pm
Forum: Appliances
Topic: Motor - Low insulation resistance
Replies: 6
Views: 5923

Motor - Low insulation resistance

Asked to connect a motor. This was a used motor so I checked the winding resistances, insulation resistance between windings and IR from windings to frame. My IRs were around 0.5M through to around 2.5M at the highest. I decided I wasn't happy to connect. My question is was this a fair judgement? I ...
by JamieP
Mon Apr 25, 2022 11:11 am
Forum: Generators and Solar
Topic: Stand alone generator supplying a single item - MEC size?
Replies: 5
Views: 4796

Re: Stand alone generator supplying a single item - MEC size?

Thanks Alec, great points to consider
by JamieP
Mon Apr 25, 2022 7:52 am
Forum: Generators and Solar
Topic: Stand alone generator supplying a single item - MEC size?
Replies: 5
Views: 4796

Re: Stand alone generator supplying a single item - MEC size?

But the definition in 4509 indicates the conductors supplying the main switchboard. Where as supplying a single load I don't have a main switchboard.
by JamieP
Sat Apr 23, 2022 5:51 pm
Forum: Generators and Solar
Topic: Stand alone generator supplying a single item - MEC size?
Replies: 5
Views: 4796

Stand alone generator supplying a single item - MEC size?

We have a proposed installation of a remote generator, supplying a VFD and then to a pump motor. I believe the generator will need an earth electrode and MEC and have looked to 4509.1 for information. With having no mains I'm struggling to understand what we size the MEC to. My only logic seems to s...
by JamieP
Sat Apr 23, 2022 1:57 pm
Forum: Standards and Legislation
Topic: ESC demarcation point
Replies: 12
Views: 6115

Re: ESC demarcation point

Thanks Alec, very helpful as always
by JamieP
Sat Apr 16, 2022 10:00 am
Forum: Standards and Legislation
Topic: ESC demarcation point
Replies: 12
Views: 6115

Re: ESC demarcation point

Yeah totally man, and I definitely understand the legal vs real world thing but it's just something that got me thinking and curious around others thought around what the words actually say and technically require rather than what is actually practical to achieve etcetc
by JamieP
Fri Apr 15, 2022 8:35 am
Forum: Standards and Legislation
Topic: ESC demarcation point
Replies: 12
Views: 6115

ESC demarcation point

I understand an ESC is completed for all work when connection is completed but I'm just curious on views on how much this makes us responsible for in some cases Disconnection and reconnecting an appliance or fitting is usually easy being on the end of the supply but I'm curious about situations such...
by JamieP
Mon Feb 21, 2022 7:14 pm
Forum: Transportable Installations
Topic: RCD requirements
Replies: 10
Views: 8139

Re: RCD requirements

My main purpose for the question above is if the limitation of 3 FSCs per RCD would apply and I understand in most cases it would never be an issue due to CIs usually being fairly small in nature but just curious from a technical point of view Also the requirements of a minimum of two RCDs, in a non...
by JamieP
Mon Feb 21, 2022 11:11 am
Forum: Transportable Installations
Topic: RCD requirements
Replies: 10
Views: 8139

Re: RCD requirements

Further question, is a CI considered a residential installation? I would assume not unless it was a sleepout or something designed for such purpose and if it's not, like simply an office, 2.6.2.4 (b) wouldn't apply? Because 2.6.2.4 (b) applies only to "in a residential installation" Obviously the ab...
by JamieP
Sun Feb 20, 2022 3:53 pm
Forum: Transportable Installations
Topic: RCD requirements
Replies: 10
Views: 8139

Re: RCD requirements

Is the CI considered its own installation? Otherwise could you consider upstream RCDs in the installation to contribute towards the minimum of two per installation when 2 or more FSCs?
by JamieP
Fri Feb 18, 2022 3:05 pm
Forum: Selection and Installation of Wiring Systems
Topic: Using the earth in control wiring as a control core?
Replies: 2
Views: 3002

Re: Using the earth in control wiring as a control core?

Thanks Alec, very in depth read And I think you can also probably conclude that regardless of trying to get around it, it's quite clear that the green/yellow is only intended to be used as an earth in many situations, this situation feels like one when you know it probably shouldn't be but you are t...
by JamieP
Thu Feb 17, 2022 1:26 pm
Forum: Selection and Installation of Wiring Systems
Topic: Using the earth in control wiring as a control core?
Replies: 2
Views: 3002

Using the earth in control wiring as a control core?

Now this one seems to get a little complex and just based on previous comments and opinion I think it'll probably be a situational basis Although probably not "good practice" (hate the term) would it be ok to use the earth core within a multicore control cable as a control core if needed? I suppose ...
by JamieP
Wed Feb 09, 2022 9:01 am
Forum: Selection and Installation of Wiring Systems
Topic: 3 Phase + N parallel in ducts
Replies: 3
Views: 2865

Re: 3 Phase + N parallel in ducts

Thank you, I was just thinking in terms of them being parallel and keeping each parallel pair together to keep them as close as possible in length

But thanks team, will look into it
by JamieP
Tue Feb 08, 2022 11:14 am
Forum: Selection and Installation of Wiring Systems
Topic: 3 Phase + N parallel in ducts
Replies: 3
Views: 2865

3 Phase + N parallel in ducts

I have 300mm² parallel conductors that I need to split across two ducts Just confirming there is no issue with this and what the best solution/split is? Haven't dealt with this so curious of information and references My thoughts are 2 phases in one and 1 phase + Ns in the other and believe this to ...
by JamieP
Sun Jan 30, 2022 1:29 pm
Forum: Transportable Installations
Topic: Connectable installations - only 90v-250v?
Replies: 7
Views: 5258

Re: Connectable installations - only 90v-250v?

I suppose as you say "connection to an external power supply that operates at a nominal voltage between 90 and 250 volts AC at standard low voltage" external power that opperates at 90-250 at SLV SLV "in respect of electricity supplied by either a single-phase MEN system or a multiple-phase MEN syst...
by JamieP
Sun Jan 30, 2022 1:08 pm
Forum: Transportable Installations
Topic: Connectable installations - only 90v-250v?
Replies: 7
Views: 5258

Re: Connectable installations - only 90v-250v?

Thanks Alec, appreciate it
by JamieP
Sat Jan 29, 2022 3:44 pm
Forum: Transportable Installations
Topic: Connectable installations - only 90v-250v?
Replies: 7
Views: 5258

Re: Connectable installations - only 90v-250v?

Apologies Alec, just had a re look over this and just to be 100% clear because it hasn't been definitely mentioned but it was ESR7 and the fact it says "connection to an external power supply that operates at a nominal voltage between 90 and 250 volts AC at standard low voltage" Incase that changes ...
by JamieP
Fri Jan 28, 2022 2:38 pm
Forum: Transportable Installations
Topic: Connectable installations - only 90v-250v?
Replies: 7
Views: 5258

Re: Connectable installations - only 90v-250v?

Ah, right, how do we know it's voltage to earth? Is that to do with the definition of standard low voltage? 230V P-N?