Haydos123
Jan 16 2019 08:12
Client has an old freestanding range on 6mm and is wanting to change it to a built in hob and oven. In the past iv usually just run existing 6mm straight to the hob and looped to the oven but sometimes is quite hard to fit a couple of 6mm wires into the hob connection block. Is there any type of junction box anyone uses that can be fitted behind everything?
Was also reading the standards and came across the position of the isolating switch. A lot of older houses have there range isolating switch mounted directly above the range itself. When changing the configuration of the range to a seperate oven/hob this would create an open cooking surface, therefore the isolating switch should really be moved to one side, 150mm from the edge of hob. Is that correct? Seems stupid considering it’s always been basically an open cooking surface and the isolating switch has always been there.
DougP
Jan 16 2019 08:25
Yes you can use a junction box behind the oven. Then you can use a 2.5mm2 to feed the oven, which usually has a smaller terminal block. Some ovens and hobs have a flex already connected, so the junction box is necessary anyway. The standard square ones are usually fine.
The switch position has been recommended "..in such a position that the user does not have to reach across the open cooking surface" for quite some time. But the "shall" requirement of 150mm to the side in 3000:2018 isn't mandatory as yet, however it would be best to move it now if possible.
Haydos123
Jan 16 2019 08:36
Thanks Doug. Yeah easier to just move the switch. And I’m never a fan of having smaller cable on a circuit that’s rated higher. I know the stove can’t physically draw anymore than 3.5kW but it never seems right putting it on a 32A breaker.
Even still, how do you get on with the junction box terminations? They would be impossible to terminate together because of there size.
DougP
Jan 16 2019 08:55
Ovens & hobs regularly come with smaller flex connected. No difference really. 1.5-2.5 on ovens, and 4mm2 on hobs. Some hobs also specify that the connecting cable is V105, so the standard TPS may not actually comply with their instructions.
And considering the normal unenclosed rating of 2.5mm2 is 30A+, I don't see why you would have a problem.
However, 3x6mm2 fit in standard single screw connector, so whatever floats your boat..
https://www.clipsal.com/Trade/Products/ ... D46flwzaUk
AlecK
Jan 16 2019 11:53
being pedantic, the switch required for a hob (or other open cooking surface" is not required to be an isolating switch, and most of them - probably all in the domestic sector - are not. They are only functional switches, and that's all they need to be.
Imported: Free standing oven and hob install
Re: Imported: Free standing oven and hob install
The wire size and fusing will be an issue. If original is 6mm this will most likely be fused at 32amps, therefore you will need to use 6mm to both hob and oven, not 2.5 as previously suggested, however you can junction either in the wall or in a junction box (which ever.is count to give the neater finish) behind the oven and have 2 6mm supplying each appliance, as these will be hard wired it will be 6mm, but if using a PCU it might become a different story
Re: Imported: Free standing oven and hob install
Balderdash.
Wiring rules clearly allow for a reduction in CCC without an additional protective device in these circumstances.
Each branch is a foxed load, so need only be sized for that load.
Wiring rules clearly allow for a reduction in CCC without an additional protective device in these circumstances.
Each branch is a foxed load, so need only be sized for that load.
Re: Imported: Free standing oven and hob install
There's a few new features on this forum Alec.
Let's call this one the "foxed" feature