Motor Overload - 4.13.2

Connection and Repair
Post Reply
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Motor Overload - 4.13.2

Post by JamieP »

"Each electric motor having a rating exceeding 370 W shall be provided with
control equipment incorporating means of protection against overload of the
motor."

Does each need its own motor overload protection? Or can you use a single motor overload for multiple items?
AlecK
Posts: 915
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: Motor Overload - 4.13.2

Post by AlecK »

Doesn't say "individual" or "dedicated" or "separate" means of protection;
or any other wording that would require the protection for one motor to be only for that motor.

Not unheard of for several motors of a system to share common control / protection devices,
but needs care to get it right
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: Motor Overload - 4.13.2

Post by JamieP »

Thanks Alec, appreciate the confirmation