4.3 connection of electrical equipment

Connection and Repair
Post Reply
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

4.3 connection of electrical equipment

Post by DougP »

There's a few examples in 4.3
But nothing that resembles installation wiring to an isolator, then more fixed/flexible wiring to a motor for example.

I think everyone just expects that 4.3.4 and fig 4.5 applies. But does it really?
You could have wiring in conduit up to the isolator, then more wiring in conduit up to the motor. Where does the installation wiring stop in that case?

TIA ;)
AlecK
Posts: 919
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 354 times

Re: 4.3 connection of electrical equipment

Post by AlecK »

The key is in the definitions of the terms [1.4.101 & 1.4.102].

4.3.4 & Fig 4.5 would apply for a PCU, ceiling rose, etc, where the final bit of wiring is flex that can be seen as being part of the appliance.
If the flex comes as part of the appliance, it's obvious.
Less so if we provide the flex; bit the definitions seal with that in most cases.

For your example; if you have fixed wiring all the way, then it's all installation wiring up to the motor terminals
Post Reply