Posted: Thu Dec 21, 2023 10:57 am
I have been asked to do an inspection on a soon to be installed animal stunning unit.
I have asked the following
"Can I be provided with all manufacturers information as per 1.6 of NZS 6116
“(b) A copy of the manufacturers or supplier’s documentation for the appliance which should contain:
(i) A list of major components (and where applicable, the voltage, frequency and current rating);
(ii) Verification that the appliance’s major components meet the requirements of this Standard or legislation applying at the time of manufacture;
(iii) Complete “as built” schematic wiring diagrams and any PLC ladder diagrams;
(iv) The results of commissioning tests;
(v) Maintenance and test instructions; and
(vi) The manufacturer’s operating procedures.”
Proof of compliance with “AS/NZS 3100” as per 3.1.6 and that transformers comply with “AS/NZS 61558.2.4 with no direct earth reference” 2.1.2 is vital." (Both NZS6116 references)
All I have been provided with is the following PDF manual. Most of it seems suitable and I have already seen this manual before but the only proof of compliance I have is the SDoC on the last page.
Am I right in the fact this isn't suitable and I should have a Certificate of Conformity stating compliance with 3100 for the appliance? The transformers supplied in the unit should also have a Certificate of Conformity?
I have asked the following
"Can I be provided with all manufacturers information as per 1.6 of NZS 6116
“(b) A copy of the manufacturers or supplier’s documentation for the appliance which should contain:
(i) A list of major components (and where applicable, the voltage, frequency and current rating);
(ii) Verification that the appliance’s major components meet the requirements of this Standard or legislation applying at the time of manufacture;
(iii) Complete “as built” schematic wiring diagrams and any PLC ladder diagrams;
(iv) The results of commissioning tests;
(v) Maintenance and test instructions; and
(vi) The manufacturer’s operating procedures.”
Proof of compliance with “AS/NZS 3100” as per 3.1.6 and that transformers comply with “AS/NZS 61558.2.4 with no direct earth reference” 2.1.2 is vital." (Both NZS6116 references)
All I have been provided with is the following PDF manual. Most of it seems suitable and I have already seen this manual before but the only proof of compliance I have is the SDoC on the last page.
Am I right in the fact this isn't suitable and I should have a Certificate of Conformity stating compliance with 3100 for the appliance? The transformers supplied in the unit should also have a Certificate of Conformity?