Double pole main switch

This includes types of overcurrent, Short Circuit and RCD protection
Post Reply
Chewbucca428
Posts: 6
Joined: Fri Jul 24, 2020 2:00 pm
Has thanked: 0
Been thanked: 0

Double pole main switch

Post by Chewbucca428 »

Hi there, as an alternative, is there any rules that says I cant combine two single pole 63amp dinrail main switches and mechanically connect them to make a double pole main switch? It's for a domestic switchboard where the ripple is on one pole and the mains is on the other. Thanks.
AlecK
Posts: 914
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: Double pole main switch

Post by AlecK »

nothing to prohibit that.
but equally no requirement for linking, either.

The rule[2.3.3.1] is minimum 1 main switch per supply, in particular 1 per safety service plus 1 for general.
In domestic there usually won't be any safety services.

Then 2.3.3. says keep them to the minimum, and for domestic one per separately metered or controlled supply.
So you have a controlled mains and one uncontrolled, so you can have 2 switches.
You can link them if you want to,and it's common practice to use linked switches, but you don't have to