Imported: RCD doesn't switch neutral

Post by DougP »

mowgli
Aug 21 2019 16:00



[shim]Is it true that an RCD that isn't required by the Standard, isn't required to switch the neutral? I've always assumed and tested for, perhaps wrongly, that all RCDs in NZ must switch the neutral.

pluto
Aug 21 2019 16:30



[shim]It is an ESR 2010 requirement reg 24(3)(a). A neutral conductor is considered a Live conductor.

JonoRTC
Aug 21 2019 17:02



[shim]ESR 24 (1): This regulation applies to any standard low voltage RCD that is used in a situation where it is required, by these regulations or any standard, to be used.

That would appear to mean that ESR 24 (3a) is specifically not required to be followed unless the RCD is used in a situation where it's required?

AlecK
Aug 21 2019 17:19



[shim]Correct; RCD that are not "required" do not have to switch the N.
The requirement to switch all live conductors is far from universal internationally.