Appendix H3.2.1, AS/NZS 3760:2010

This includes types of overcurrent, Short Circuit and RCD protection
Post Reply
Spannerz
Posts: 3
Joined: Fri Mar 12, 2021 5:27 am
Answers: 0
Has thanked: 0
Been thanked: 0

Appendix H3.2.1, AS/NZS 3760:2010

Post by Spannerz »

Hello,

Can anyone confirm, Appendix H3.2.1 (This is probably an already known typo.)

"The test may be preformed on a single-phase supply"

Should read,

"The test may be preformed on a three-phase supply"


Thanks.
AlecK
Posts: 912
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 351 times

Re: Appendix H3.2.1, AS/NZS 3760:2010

Post by AlecK »

No.

This is really an Exception to the general rule [3.2] that 3-phase RCDs must be tested on a 3-phase supply.
It relaxes that general rule so that a single-phase supply can by used for the test, subject to either of the conditions.
Spannerz
Posts: 3
Joined: Fri Mar 12, 2021 5:27 am
Answers: 0
Has thanked: 0
Been thanked: 0

Re: Appendix H3.2.1, AS/NZS 3760:2010

Post by Spannerz »

OK. Yes, the method is fine.


Should it read

"...preformed FROM a single-phase supply"

Fine if you read it consecutively from 3.1 through to 3.2.1 (b)..Note 3, Before completely skipping Appendix i which seems to be missing altogether..?

Code: Select all

[H3.2]..."For three-phase RCDs"....
.......[3.2.1] ..."test maybe preformed on a single phase supply"...
...............(a)....
...............(b)....
...................Note 1....
...................Note 2....
...................Note 3....