Hello,
Can anyone confirm, Appendix H3.2.1 (This is probably an already known typo.)
"The test may be preformed on a single-phase supply"
Should read,
"The test may be preformed on a three-phase supply"
Thanks.
Appendix H3.2.1, AS/NZS 3760:2010
Re: Appendix H3.2.1, AS/NZS 3760:2010
No.
This is really an Exception to the general rule [3.2] that 3-phase RCDs must be tested on a 3-phase supply.
It relaxes that general rule so that a single-phase supply can by used for the test, subject to either of the conditions.
This is really an Exception to the general rule [3.2] that 3-phase RCDs must be tested on a 3-phase supply.
It relaxes that general rule so that a single-phase supply can by used for the test, subject to either of the conditions.
Re: Appendix H3.2.1, AS/NZS 3760:2010
OK. Yes, the method is fine.
Should it read
"...preformed FROM a single-phase supply"
Fine if you read it consecutively from 3.1 through to 3.2.1 (b)..Note 3, Before completely skipping Appendix i which seems to be missing altogether..?
Should it read
"...preformed FROM a single-phase supply"
Fine if you read it consecutively from 3.1 through to 3.2.1 (b)..Note 3, Before completely skipping Appendix i which seems to be missing altogether..?
Code: Select all
[H3.2]..."For three-phase RCDs"....
.......[3.2.1] ..."test maybe preformed on a single phase supply"...
...............(a)....
...............(b)....
...................Note 1....
...................Note 2....
...................Note 3....