2.5.7.2.3 Discrimination examples (b) and (c)
Posted: Sun Apr 19, 2020 3:47 pm
"Discrimination on overload and instantaneous operation may be
deemed to be provided when C1 ≥ 2 × C2, e.g. C1 curve 63 A
with C2 curve 32 A (see Figures 2.11 and 2.12.)"
This says a 63A with a 32A but using the method of calculation 2*32=64 so a 63A MCB is not ≥ a 32A MCB
"(A) the overload setting of C1 ≥1.6 × C2, e.g. 1000 A with 630
A; and
(B) the instantaneous setting of C1 ≥1.6 × C2, e.g. C1=5 ×
1000 A with C2=5 × 630 A."
630*1.6=1008
630*5*16=5040
1000*5=5000
Same here for the 250 to 799 requirements
Am I missing something or screwing something up or is this some sort of mistake? I highly doubt it's a mistake when it happens in 2 cases
deemed to be provided when C1 ≥ 2 × C2, e.g. C1 curve 63 A
with C2 curve 32 A (see Figures 2.11 and 2.12.)"
This says a 63A with a 32A but using the method of calculation 2*32=64 so a 63A MCB is not ≥ a 32A MCB
"(A) the overload setting of C1 ≥1.6 × C2, e.g. 1000 A with 630
A; and
(B) the instantaneous setting of C1 ≥1.6 × C2, e.g. C1=5 ×
1000 A with C2=5 × 630 A."
630*1.6=1008
630*5*16=5040
1000*5=5000
Same here for the 250 to 799 requirements
Am I missing something or screwing something up or is this some sort of mistake? I highly doubt it's a mistake when it happens in 2 cases