Motor Insulation Resistance test
Posted: Mon Nov 29, 2021 6:38 am
I have an old ( 8y+) submersible pump motor that had been disconnected for more than 6 months. I wanted to check and see if it tested ok and so did an insulation resistance test between phase and earth. I was expecting to get a reading either good or bad, however something unexpected happened ā the tester immediately commenced with a low reading (0.4M ohm) and then started climbing up to around 5M Ohm. I removed the test lead and then re-applied it ā the meter showed that it could not apply a test because there was a voltage of 54V present. This had to be discharged before the test could be reapplied (with similar results).
All in all it tests more like Iād expect from a capacitor and less like a motor. Has anyone come across this before and found an explanation for it? What would you say about the motor condition? The fact that it stores charge suggests to me that the insulation is fine, however because of the low initial reading I'd expect high inrush currents that may be problematic.
Any thoughts suggestions would be appreciated
All in all it tests more like Iād expect from a capacitor and less like a motor. Has anyone come across this before and found an explanation for it? What would you say about the motor condition? The fact that it stores charge suggests to me that the insulation is fine, however because of the low initial reading I'd expect high inrush currents that may be problematic.
Any thoughts suggestions would be appreciated