Can an RCBO 1P+N be used in the switchboard of a caravan if the RCBO switches active and neutral?

DougP
Oct 11 2019 15:59
RCBO small.jpg
Yes, and that's all you need.



AlecK
Oct 11 2019 17:03

as long as it's 16 A.

EnosM
Oct 11 2019 17:39

Thanks for your replies. I'm curious regarding the "1P+N" if someone plugged in a lead that had phase and neutral reversed

DougP
Oct 11 2019 19:01

It will still provide exactly the same overload and earth leakage protection, as long as there aren't any other faults in the installation.

pluto
Oct 11 2019 20:42

That only occurs in true double pole RCBOs which are in a double width (36 mm wide) package.
Many single width RCBOs are only a single pole main contact (active) with an early make or late break neutral pole.

DougP
Oct 11 2019 21:45

There is no difference. It opens both poles instantaneously.

The overload protection might only operate on the active pole, but that makes no difference even with reverse polarity.