Imported switchgear IEC standards

Post Reply
Dan L
Posts: 158
Joined: Tue May 19, 2020 10:00 pm
Has thanked: 4 times
Been thanked: 3 times

Imported switchgear IEC standards

Post by Dan L »

Technically is IEC Switchgear acceptable to use in NZ. For a standard installation and for CI

Photo attached.

Rcd 30ma Type A
Attachments
Screenshot_20230503_221142_com.android.chrome.jpg
Dan L
Posts: 158
Joined: Tue May 19, 2020 10:00 pm
Has thanked: 4 times
Been thanked: 3 times

Re: Imported switchgear IEC standards

Post by Dan L »

Piic attached
Attachments
Screenshot_20230503_141911_com.google.android.gm.jpg
AlecK
Posts: 914
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: Imported switchgear IEC standards

Post by AlecK »

All such devices are imported; nobody makes this stuff in NZ.

As to whether compliance with IEC Standards is acceptable; check Schedule 4 (Part 5) of ESRs.

However note that RCDs being installed under Wiring Rules are required to comply with one of the Standards cited in 2.6.2.2.
These are all AS/NZS Standards that are based closely on IEC Standards of same number, with some particular changes for Oz / NZ


Circuit protective devices are subject to ESRs 80, 83, & 84;
and in my view this applies not only to items sold / supplied as individual items, but also to items imported as part of a new / used CI.

This switchgear appears to be ex-UK, and I don't believe there is anything non-compliant it; except that it may not have been issued an Approval.
The RCD is marked as Type A.
However I would question whether the required current limitation is in place.