I’m working in with an electrician who is installing a PV system, he’s doing the installation, I’ll be doing inspection.
I’ve been advised they’re installing three phase enphase/micro-inverters that are designed for the American market, therefore operate at 110/220VAC. The switchboard is apparently supplied by a grid simulator (not entirely sure what this is), but have been advised the switchboard that the micro-inverters are to be connected to is going to operate at 110/220VAC.
I just have a few uncertainties around the compliance of such an arrangement, it’s somewhat unfamiliar territory.
Is such an arrangement a part 1 installation, and would therefore require a certified design? I’m uncertain about the wiring identification, the electrician has advised me the wiring supplying the inverters is US colouring, is this acceptable? They’re intending on using 230/400VAC standard NZ switchgear, is it okay to use this at 110/220V? I imagine this would be okay as the voltage rating of the switchgear will exceed what it will be operating at.
It sounds like a pretty unusual arrangement. It’s being installed at a research & development facility.
Any advice much appreciated. Thanks!
US enphase inverters
- gregmcc
- Site Admin
- Posts: 189
- Joined: Sun Apr 12, 2020 4:45 pm
- Has thanked: 18 times
- Been thanked: 49 times
Re: US enphase inverters
Part 1 installations *must* be a certified design, Part 2 installations can be a certified design but don't have to be.
Sounds like a bit of a can of worms here, It would be a good idea to insist on a certified design so it very clear what is been done and why and how compliance is going to be achieved.
110/220V doesn't fall with in the standard voltages, I think there is some thing in the ESR's about the use of non standard voltages.
Sounds like a bit of a can of worms here, It would be a good idea to insist on a certified design so it very clear what is been done and why and how compliance is going to be achieved.
110/220V doesn't fall with in the standard voltages, I think there is some thing in the ESR's about the use of non standard voltages.