Connection of PV exposed conductive parts
Posted: Sun Sep 13, 2020 8:32 pm
The bottom of 4.4.2.2 says
"If the earthing is for bonding requirements only then the array earth may be connected to
the installation earth via the PCE protective earth so long as removing the inverter for
maintenance:
(i) does not remove the earth connection; and
(ii) provided the PCE protective earth is of adequate cross-section according to the
requirement of Figure 4.3."
Am I reading this right that I may connect my earth to the protective earth in the cable that feeds the inverter? But I can only do so if the PEC in that cable also meets the minimum size requirements of Fig 4.3
So if I have a 4mm2 earth for the exposed conductive parts, I can only connect to the PEC at the inverter if it also was at least 4mm2?