Page 1 of 1

PCE Earth Connection

Posted: Tue Sep 29, 2020 1:33 pm
by JamieP
Screenshot_20200929-132857_Drive.jpg
Is connecting to the earth bar compliant? Or must I physically connect to the main earth?

If the latter, what's the best device to use? Or is terminating into the same tunnel terminal or lug as the main earth sufficient/compliant?

Re: PCE Earth Connection

Posted: Tue Sep 29, 2020 5:14 pm
by AlecK
"3000" 5.5.2 covers acceptable methods of connecting PECs; Illustrated in Fig 5.3.
It follows that connecting to the earth bar is compliant.
That said; the "should" in "5033" 4.4.2.1 indicates connecting directly to the MEC is preferred.

If you do connect a PEC to the MEC directly, a type of connection that doesn't require cutting / joining the MEC should be used - eg a "line tap"

Re: PCE Earth Connection

Posted: Tue Sep 29, 2020 6:46 pm
by JamieP
Ah, thank you, I had missed that it was a should but regardless good to know