PV Inverter incorrectly rated for the PV panels

Posted: Wed Dec 09, 2020 3:00 pm
by PeteRig
I have a situation where a PV inverter's label has ratings less than the PV panel ratings:
The short circuit current rating (Isc) and the Max power current (Imp)of the PV panel is higher than the Inverter ratings.

The inverter engineer's have said that the inverter will be find for these currents even though the inverter label says different as well as the data sheet for the inverter.

Should I ask for something in writing from them stating that the inverter will be ok or insist on the inverter been upgraded?

Thanks

Re: PV Inverter incorrectly rated for the PV panels

Posted: Wed Dec 09, 2020 3:56 pm
by AlecK
Nothing you get from them will cover your bum if things go wrong.
You're the one who'll be signing the CoC, and who will therefore be open to come-back from the end-user.

Re: PV Inverter incorrectly rated for the PV panels

Posted: Wed Dec 09, 2020 3:58 pm
by AlecK
Correction: nothing short of a Certified design as per ESR 58 will cover your bum
So if you've got what amounts to a CD, all you have to do is follow it.

Re: PV Inverter incorrectly rated for the PV panels

Posted: Wed Dec 09, 2020 4:00 pm
by PeteRig
Ok, thanks Alec