I am doing max demand calculations for a shed and there is to be a 16A socket outlet set up in accordance with 3001 but I'm just wondering what value I use for max demand?

B ii and b iii don't explicitly apply

Possibly M? But what can I assess?

Or because the connectable is current limited by a 16A device treat it as a full 16A?
AlecK
Posts: 916
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: Max Demand for Connectable Installations

Post by AlecK »

app A of 3001 provides guidance.
But if you allow the full 16 A you can't be wrong
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: Max Demand for Connectable Installations

Post by JamieP »

I was under the impression App A was for caravan parks etcetc

I am simply doing a supply to a shed and putting a single connection point

Agree though, allowing the full 16A seems to be the best option
AlecK
Posts: 916
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: Max Demand for Connectable Installations

Post by AlecK »

yes the appendix is specifically for caravan parks, but it provides a basis for assessing in other situations that is likely to be closer to reality than treating this point as just a socket outlet.
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: Max Demand for Connectable Installations

Post by JamieP »

Understood, thanks Alec