Sub-main to domestic shed: Minimum size?
Posted: Tue May 16, 2023 9:43 pm
A small shed on a carport requires power for 1 power point and 3 lights. I don't know if the owner prefers overhead or underground cable route yet for the 3m gap between the house and shed. Please can someone let me know if there is a minimum cable size to a sub-main? From 3.12.2.2 it looks like 6mm for aerial.
3.12.2.2 Minimum size
The minimum size of aerial conductors shall be as follows:
(a) Copper and aluminium conductors Copper or aluminium conductors installed as aerial conductors shall have not less than seven strands and shall be not smaller than 6 mm2 for copper or 16 mm2 for aluminium.
What about underground? Thank you.
3.12.2.2 Minimum size
The minimum size of aerial conductors shall be as follows:
(a) Copper and aluminium conductors Copper or aluminium conductors installed as aerial conductors shall have not less than seven strands and shall be not smaller than 6 mm2 for copper or 16 mm2 for aluminium.
What about underground? Thank you.