Clauses that need to be amended or clarified

Post by DougP »

How about note 3 of 6.2.1
Shouldn't that also apply to equipment recessed into walls? Such as wall mounted fans?
AlecK
Posts: 945
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 369 times

Re: Clauses that need to be amended or clarified

Post by AlecK »

I don't think so.
There's a considerable difference in risk between a wall limiting a Zone, and a ceiling limiting a Zone.
Water seldom falls upwards, and splash seldom reaches the ceiling
(even when the ceiling is low enough to replace the default height measurement as limit of Zone).