Post by PeteRig »

In AS/NZS 3000:2007 Fig 5.2 shows a HV Customer Substation supplying a Main Swb (no MEN link) are the conductors supplying this swb "mains" ?
ESR reg 4 has the definitions of "mains" and "mains work" both refer to connecting the conductors to a MEN switchboard.
If the POS is the substation then, no? Have I just answered my own question?
Thanks Peter
AlecK
Posts: 920
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 356 times

Re: Mains Work

Post by AlecK »

The problem is that ESRs don't allow for the fact that sometimes the MSB is not actually an MEN swbd, because the MEN link is relocated to the (dedicated) sub as permitted by 5.3.5.1 & illustrated in Fig 5.2.
Therefore technically there may be no "mains" as defined in ESRs.
However it would be most unwise to do anything other than treat the A(s) & N conductors from sub as "mains", and the PEC as MEC.

The intent is clear, even if the writers of ESRs (mostly lawyers rather than people who know the subject) didn't get the words quite right.
These users thanked the author AlecK for the post:
PeteRig (Wed Sep 22, 2021 12:43 pm)
Rating: 16.67%
PawPatrol
Posts: 27
Joined: Thu Jun 04, 2020 8:42 pm
Has thanked: 1 time
Been thanked: 1 time

Re: Mains Work

Post by PawPatrol »

PeteRig wrote:
Wed Sep 22, 2021 11:58 am
In AS/NZS 3000:2007 Fig 5.2 shows a HV Customer Substation supplying a Main Swb (no MEN link) are the conductors supplying this swb "mains" ?
ESR reg 4 has the definitions of "mains" and "mains work" both refer to connecting the conductors to a MEN switchboard.
If the POS is the substation then, no? Have I just answered my own question?
Thanks Peter
You have answered your own question, some of the conductors in the main swb (if before men board) will be mains until they connect to the men board.
AlecK
Posts: 920
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 356 times

Re: Mains Work

Post by AlecK »

The exact way the terms apply depends on which of 3 Exceptions to clause 5.3.5.1 is being used.
Fig 5.2 illustrates all three, but does not indicate where the POS is (ie where the "installation" starts).
It doesn't need to; because that's not relevant to understanding the requirements of the Standard

If the substation is part of works, Exception 3 applies; and the installation's MSB has no MEN. Instead the MEN is within the substation.
The POS will be downstream of the MEN, and it follows that there will be no " fittings forming part of the installation that are used for the supply of electricity to the MEN swbd that is closest to the point of supply" (ie, nothing that fits the definition of "mains").

Another possibility is that the installation is fed at HV; and the POS is upstream of the (dedicated) substation.
Exception 1 applies; and the "mains" will include (most of) the substation.

The other relevant clause is 5.5.1.1, which allows for the installation's MEC to be run to a sub instead of to an earth electrode.