Reg 67 (1)(e) "the type of supply system that the installation or part installation is safe
to connect to"

Can someone confirm what this actually wants? Is simply putting MEN supply enough? Does it want TN-C-S? Does it want voltage and Hz values?

Just wondering what's actually sufficient
User avatar
gregmcc
Site Admin
Posts: 189
Joined: Sun Apr 12, 2020 4:45 pm
Answers: 0
Has thanked: 18 times
Been thanked: 49 times

Re: Type of supply system for CoC

Post by gregmcc »

On my COC's I have "Supply System 230V/400V MEN"
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Re: Type of supply system for CoC

Post by DougP »

230V, 1P MEN
400/230V 3P MEN
etc
AlecK
Posts: 912
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 351 times

Re: Type of supply system for CoC

Post by AlecK »

The type of supply system is about what form of earthing is used.
It's generally "MEN"; because that's what's normally used for both distribution and installations in NZ.

MEN is the particular variant of TN-C-S used in NZ (and Oz).
TN for "terra neutral"; ie the neutral is earthed; and -C-S designating how it is earthed.
C for "common" conductor performing both neutral and earthing functions, in the network and for mains (and some submains);
S for (separate" conductors performing these functions within the installation.
As explained, in brief, in clause 5.1.3

Number of phases isn't important; what they want to know is whether the installation / part-installation is designed for MEN;
or if it's not, what earthing system it is designed for