NZS6116:2006 Transformer supplying electrodes
Posted: Wed Apr 12, 2023 1:44 pm
I have been supplied with a 230V/550V transformer to supply the electrodes for the neck and nose in a beef box stunner.
The unit complies with AS/NZS61558.1
4.5 indicates compliance with table 2, 2 of table 2 says is in compliance with AS/NZS61558.2.4
Table 2 references clause 2.1.2 for this
If I look at 2.1.2 it mentions "equipment not protected by barriers shall be supplied from an isolating class transformer complying with AS/NZS61558.2.4 with no direct earth reference unless specifically allowed in section 3"
I believe the electrodes in my case have sufficient barriers
Is compliance with AS/NZS61558.1 enough since my equipment is protected by barriers?