NZS6116:2006 Black EB Conductors

Post by JamieP »

I have been told by another inspector that all the conductors of the equipotential bonding network need to be black.

I disagree and believe green yellow should be used in accordance with 3.4.3 and that black should be reserved for metalwork being used as an electrode and I assume this is to do with the electrode being a live part.

I'm pretty happy around my judgement here but just making sure I am not missing anything.
AlecK
Posts: 919
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 356 times

Re: NZS6116:2006 Black EB Conductors

Post by AlecK »

Correct that most EBCs must be green / yellow; with only those for metalwork that is an electrode of the appliance being black.
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: NZS6116:2006 Black EB Conductors

Post by JamieP »

Thank you, exactly as I believed