110V appliances and outlets

Post Reply
Fatboy
Posts: 1
Joined: Tue Apr 14, 2020 8:36 am
Has thanked: 3 times
Been thanked: 0

110V appliances and outlets

Post by Fatboy »

I have a customer who is adamant they are having 110V appliances in their kitchen. Is there anything prohibiting having 110V sockets run off a 110V 60Hz inverter. The house will supposedly be off grid, although I cant see this being possible due to the size of the house and the desired appliances.
AlecK
Posts: 263
Joined: Thu Apr 16, 2020 11:24 am
Answers: 1
Has thanked: 1 time
Been thanked: 87 times

Re: 110V appliances and outlets

Post by AlecK »

I don't believe there is any rule to prohibit this arrangement; regardless of on / off grid.

Would need to pay close attention to short circuit protection & fault protection;
and the absolute requirement for final subcircuits supplying sockets / lighting to be RCD-protected
(I strongly suspect you won't find any Approved & SDoCed RCDs for 110 V).

half the voltage, so double the current, so bigger conductors; and multiply again for voltage drop.
Then all directly-connected, with high-current switches.
plus the inverter - sized for max demand of the part-installation
and a DB - since they won't all fit on one final subcircuit.
Seems a lot of trouble & cost just to be able to run American? appliances that aren't supported in NZ.
These users thanked the author AlecK for the post:
Fatboy (Fri Oct 16, 2020 6:29 am)
Rating: 16.67%
Post Reply