lightning protection system certification

Post Reply
Knuckle
Posts: 1
Joined: Wed Jul 21, 2021 1:43 pm
Has thanked: 2 times
Been thanked: 0

lightning protection system certification

Post by Knuckle »

Hi All,

Been asked about the certification (COC and ROI) of a lightning protection system once we install it. My first thought was installing down conductors and the bonding/earthing cables would be considered PEW and require a CoC but its not a low voltage installation so now thinking NZS3000 would not apply? any thoughts guys n gals..?
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: lightning protection system certification

Post by JamieP »

Yeah good point.

Is it PEW under Schedule 1 of ESRS is probably the main question.

Does it meet the exception for being a supply not exceeding ELV?
These users thanked the author JamieP for the post:
Knuckle (Fri Mar 01, 2024 7:11 am)
Rating: 16.67%
AlecK
Posts: 915
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: lightning protection system certification

Post by AlecK »

Look at definition of ;electrical installation";
Remembering to use the one in our Act, not the one in "3000".
Hard to see how a lighting protection system fits into that, so I reckon not PEW
These users thanked the author AlecK for the post:
Knuckle (Fri Mar 01, 2024 7:11 am)
Rating: 16.67%
Post Reply