power points under eves

Post Reply
Nathan
Posts: 38
Joined: Sun Apr 12, 2020 11:12 pm
Has thanked: 6 times
Been thanked: 0

power points under eves

Post by Nathan »

Recently I have seen several houses with IP53 power points mounted under the house eves with the mounting block that would normally be attached to the wall screwed to the eves.

Technically its out of the rain so would comply however once you think about people waterblast and wash down the outside of the house the chance of someone spraying water directly into the outlet it pretty high, plus you cant use the drain holes in the mounting block.
Personally I wouldnt do it but im just wondering what everyone else thinks
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Re: power points under eves

Post by DougP »

3000:2018 has a 30deg angle zone under an overhang, where no IP rating is required. Cleaning/waterblasting isn't taken into consideration.
3000:2018A1 4.1.3 & Fig 4.1
These users thanked the author DougP for the post:
Mazdaman (Sun Apr 11, 2021 11:06 am)
Rating: 16.67%
PeteRig
Posts: 149
Joined: Sat Apr 25, 2020 2:38 pm
Has thanked: 55 times
Been thanked: 31 times

Re: power points under eves

Post by PeteRig »

I suppose also Nathan you cant stop people and their actions, if someone wants to waterblast a power outlet you cant stop them
Nathan
Posts: 38
Joined: Sun Apr 12, 2020 11:12 pm
Has thanked: 6 times
Been thanked: 0

Re: power points under eves

Post by Nathan »

Thanks thats interesting.
So in theory they could be a normal PDL 692 power point on a mounting block in that case which would probably look better.
Cheers guys sounds like its one of those things that doesnt feel right but complies
User avatar
gregmcc
Site Admin
Posts: 189
Joined: Sun Apr 12, 2020 4:45 pm
Has thanked: 18 times
Been thanked: 49 times

Re: power points under eves

Post by gregmcc »

You can only account for "normal" conditions, pretty much any socket, IP53 or IP56 isn't going to standup to been water blasted.
t92300
Posts: 14
Joined: Mon Apr 13, 2020 8:47 pm
Location: Apprentice
Has thanked: 19 times
Been thanked: 0

Re: power points under eves

Post by t92300 »

Nathan wrote:
Sun Apr 11, 2021 2:06 pm
Thanks thats interesting.
So in theory they could be a normal PDL 692 power point on a mounting block in that case which would probably look better.
Cheers guys sounds like its one of those things that doesnt feel right but complies
Why even use a mounting block? Just cut a hole in the hardy board and put it in a flush box.
AlecK
Posts: 914
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: power points under eves

Post by AlecK »

You can't control stupid.
Even duct tape doesn't fix that