Main earth size for mains in parallel

Post by Dan L »

It states main earth shoukd be sized to the largest active conductor

But what if active conductors are in parallel. I feel like the actives csa should be combined and main earth relevant to that but the wording does not read like that.

But in practise not combining the actives doesn't not seem correct.

Help on this one much appreciated
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Answers: 0
Has thanked: 92 times
Been thanked: 18 times

Re: Main earth size for mains in parallel

Post by JamieP »

5.3.3.1.2 may be under protective earth conductors but I believe the information at the bottom of this clause is more relivant to using table 5.1 rather than strictly to PECs, I'd definitely apply this same logic to MECs despite not being mentioned in 5.3.3.2
AlecK
Posts: 912
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 351 times

Re: Main earth size for mains in parallel

Post by AlecK »

Yes, for mains in parallel it's the combined CSA that counts;
the CSA of each phase is 2 x CSA of the individual conuctors that make up the phase
Eg 2 x 25 mm Cu = 50 mm total, so MEC 16 mm2
Dan L
Posts: 158
Joined: Tue May 19, 2020 10:00 pm
Answers: 0
Has thanked: 4 times
Been thanked: 3 times

Re: Main earth size for mains in parallel

Post by Dan L »

Thanks. I was hoping for that response
Dan L
Posts: 158
Joined: Tue May 19, 2020 10:00 pm
Answers: 0
Has thanked: 4 times
Been thanked: 3 times

Re: Main earth size for mains in parallel

Post by Dan L »

Thanks.

I think 3000 wording is a bit of a let down here.
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Re: Main earth size for mains in parallel

Post by DougP »

Isn't this clear enough?

"Where the active conductor comprises a number of conductors, connected
in parallel, the earthing conductor shall be determined in relation to the
summation of the cross-sectional areas of the individual conductors forming
the largest active conductor to be protected."
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Answers: 0
Has thanked: 92 times
Been thanked: 18 times

Re: Main earth size for mains in parallel

Post by JamieP »

Doug I think it's the fact that's in clause 5.3.3.1.2 under PECs where as 5.3.3.2 for MECs doesn't have that as mentioned above

Although as I said i believe that logic was more intended for using Table 5.1 rather than strictly related to PECs