Hey fellas,
This was addressed in the old forum but what are some of your guys methods of bonding to the rebar in a concrete slab?
I remember Alec had a method using an earth rod but can't remember the details...
AlecK
Posts: 919
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 355 times

Re: Bonding of Rebar in Slab

Post by AlecK »

For using the slab as the electrode:
Cut a standard galvanised electrode into 2 or 3 pieces, bend each piece 90 deg, and tie one leg to the re-bar - 2 or 3 ties - with the other leg coming up where a bottom plate will be.
Use a flush box & labelled blank plate to provide the required access for inspection & testing.

The point of using galv rod is that it's protected against corrosion; whereas re-bar isn't.
And being in a protected place within the wall cavity, no further anti-corrosive action is needed


Works for bonding also, without need for access point.
These users thanked the author AlecK for the post:
eTeam (Fri Jun 26, 2020 1:57 pm)
Rating: 16.67%
User avatar
eTeam
Posts: 8
Joined: Mon Apr 20, 2020 7:40 pm
Location: Pukekohe
Has thanked: 2 times
Been thanked: 0

Re: Bonding of Rebar in Slab

Post by eTeam »

Awesome thanks mate
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: Bonding of Rebar in Slab

Post by JamieP »

There are ready made products from a number of manufactures but they are fairly pricey

Wricons and LPINZ to name a few