Nominal size

Post Reply
Dan L
Posts: 158
Joined: Tue May 19, 2020 10:00 pm
Has thanked: 4 times
Been thanked: 3 times

Nominal size

Post by Dan L »

Scenario...

120al mains with 50mm cu tails

160amp service fuse

What is the nominal size of active here?

Mains are not sized larger for vd
Dan L
Posts: 158
Joined: Tue May 19, 2020 10:00 pm
Has thanked: 4 times
Been thanked: 3 times

Re: Nominal size

Post by Dan L »

To put it simply for choosing the main earth size and the PE for switchboard can I work off tails?

( forget about PE selection by calculation in this question)
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Re: Nominal size

Post by DougP »

IMO, according to the wording of "the largest active conductor of the consumers mains", you should go for the earth rated for the size of the 120mm² Al.
The 50mm² Cu, only has a suitable CCC for that service because it's rated as spaced within a switchboard. It's not big enough for the whole mains run. So if the mains was 70mm², you would be at the same 25mm² MEC anyway. So that's the size I would use.
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: Nominal size

Post by JamieP »

Yeah I'd go with what Doug said and go by the largest part

Or attempt calculation 5.3.3.1.3 and see what happens haha
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Re: Nominal size

Post by DougP »

JamieP wrote:
Fri Jan 29, 2021 10:13 am
Or attempt calculation 5.3.3.1.3 and see what happens haha
ain't nobody got time for that :lol:
AlecK
Posts: 919
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 355 times

Re: Nominal size

Post by AlecK »

Agree with DougP that the tails may possibly be undersized.
Not enough info given to be sure; as CCC depends not only on conductor material;
but also insulation type, and installation conditions (for worst part of the run).
however as long as they do have CCC adequate for load to be carried, and are protected against overload;
then that's the size to apply when selecting MEC size from Table 5.1.

The rating of supply fuses is only relevant IF they are being used as the overload protection for the mains