I’ve had another electrician ask me about the use of a shipping container (that has exits at each end) to house a switchboard that has a 1000A/three phase supply.

I don’t believe it complies with 2.9.2.2(c)(ii). Even though it has an alternative exit, I imagine in most circumstances this alternate exit will be shut (can only be opened on the outside), making it ineffective? Thoughts?

Photo of container attached

Thanks.
Attachments
588454BB-5286-45EA-BC41-DD2D22A36D35.png
F6155DFC-0F86-4D10-8ADA-95F57257E0ED.png
F2114BCF-7AD3-4CD8-8FA0-B9515B1E0229.png
AlecK
Posts: 914
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: Large Switchboard in Container

Post by AlecK »

I agree.
It's over the trigger point for requiring a 2nd exit; and ALL doors in exit paths must open out without use of key/tool
morporks
Posts: 2
Joined: Thu Feb 16, 2023 8:40 am
Has thanked: 0
Been thanked: 0

Re: Large Switchboard in Container

Post by morporks »

Have seen many of these. The doors get changed so they can be opened from the inside
jaimin.parmar
Posts: 2
Joined: Fri Mar 03, 2023 2:21 pm
Has thanked: 1 time
Been thanked: 0

Re: Large Switchboard in Container

Post by jaimin.parmar »

I have seen the portable MCCs been done in containers. In fact I will be reviewing the electrical design of 600A Portable MCC soon.

As long as the door space is adequate and inline with the 2.10.2 it is still compliable to have such MCCs

As the containers are made of metal, sufficient ventilation will be necessary to be considered.