Post by ShaneR »

Hi all

When single core power cable(s) would enter into a metal enclosure we used cut a square hole and cover it with a large aluminium plate then drill holes through that.

Its this still a requirement?

Does it make any difference?

Thanks
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: Single core cable entry into metal enclosure

Post by JamieP »

I believe it's to do with Eddy Currents, don't know a lot about it myself but section 3.9.10 covers it I believe
These users thanked the author JamieP for the post:
ShaneR (Mon May 18, 2020 4:42 pm)
Rating: 16.67%
PeteRig
Posts: 152
Joined: Sat Apr 25, 2020 2:38 pm
Has thanked: 55 times
Been thanked: 33 times

Re: Single core cable entry into metal enclosure

Post by PeteRig »

Yeah still a requirement, electrical theory doesn't change, as Jamie has pointed out covered in section 3.9.10.
Slotting metal or fitting AL plates "Stops eddy and his mates"
AL plates make it easy to drill out for the cable glands, remove the plate from the board and no mess inside the board!
These users thanked the author PeteRig for the post:
ShaneR (Mon May 18, 2020 4:42 pm)
Rating: 16.67%
ShaneR
Posts: 33
Joined: Wed Apr 22, 2020 5:31 pm
Has thanked: 31 times
Been thanked: 2 times

Re: Single core cable entry into metal enclosure

Post by ShaneR »

Thanks for that

I had a read, I didn't know that the slot width is proportional to cable size (20%).

Question: Does single TPS cable(s) need to be run in trefoil?

Looks like single core neutral screen does
AlecK
Posts: 924
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 357 times

Re: Single core cable entry into metal enclosure

Post by AlecK »

Whenever you're intending 3-phase supply spread across multiple cables, you should take steps to minimise the possible adverse effects of the overall electromagnetic fields. The higher the current; the more important this is.
These users thanked the author AlecK for the post:
ShaneR (Tue May 19, 2020 7:37 am)
Rating: 16.67%
User avatar
Sarmajor
Posts: 8
Joined: Fri Apr 17, 2020 6:57 pm
Location: Morrinsville
Has thanked: 0
Been thanked: 1 time

Re: Single core cable entry into metal enclosure

Post by Sarmajor »

There is no logical electrical reason to trefoil single core N/S cables. The magnetic fields of these currents are cancelled by the neutral screen.
ShaneR
Posts: 33
Joined: Wed Apr 22, 2020 5:31 pm
Has thanked: 31 times
Been thanked: 2 times

Re: Single core cable entry into metal enclosure

Post by ShaneR »

Sarmajor wrote:
Tue May 19, 2020 6:30 pm
There is no logical electrical reason to trefoil single core N/S cables. The magnetic fields of these currents are cancelled by the neutral screen.
Have a look at 3.9.10.3
AlecK
Posts: 924
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 357 times

Re: Single core cable entry into metal enclosure

Post by AlecK »

1C +N/S is not a "single-core" cable; it's a form of multi-conductor cable.
Refer also clause 3.3.5 of "3008.1.2; which says how N/S is to be treated for establishing CCC.

And the screen is not a "metal sheathing". 3.9.10.3 covers things like MIMS cable.
These users thanked the author AlecK for the post:
ShaneR (Wed May 20, 2020 1:29 pm)