Hypothetical..

If there was a main switchboard on a pole near the property boundary (configured correctly as a MSB), and the only outgoing circuit was a submain to a house, can the submain protective device also be the main switch?

In other words, there is only one 63A circuit breaker on the switchboard marked as "Main Switch" and that provides O/L and SC protection for the submain.
Or is there a requirement for them to be separate devices?
AlecK
Posts: 912
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 351 times

Re: Main switchboard, main switch

Post by AlecK »

No requirement for separate devices, as long as there's only one outgoing circuit and appropriate labelling is in place indicating all functions.
A third function could be overload protection for the mains.
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Re: Main switchboard, main switch

Post by DougP »

Thanks. Yes I thought it was probably fine. Similar to a transportable switchboard with only one RCBO.
Good to get a second opinion though ;)
AlecK
Posts: 912
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 351 times

Re: Main switchboard, main switch

Post by AlecK »

Sometimes a Standard specifically states that functions may be combined; but the basic rule is that if it ain't banned it's permitted.