Cable tray

Post Reply
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Cable tray

Post by DougP »

Does it need to be earthed?
20200608_154400.jpg
User avatar
gregmcc
Site Admin
Posts: 189
Joined: Sun Apr 12, 2020 4:45 pm
Has thanked: 18 times
Been thanked: 49 times

Re: Cable tray

Post by gregmcc »

for double insulated conductors no, but for good practice yes, the photo is a good example
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Re: Cable tray

Post by DougP »

gregmcc wrote:
Wed Nov 11, 2020 5:34 am
for double insulated conductors no, but for good practice yes, the photo is a good example
That's not going to help the guy on the forklift if he gets off it when the forklift is live though. The cables were only damaged on the forklift side, not the back.
And any electrical worker getting up there to repair, should be isolating it before working on it. With that number of circuits, the only option was isolating the whole building.
User avatar
gregmcc
Site Admin
Posts: 189
Joined: Sun Apr 12, 2020 4:45 pm
Has thanked: 18 times
Been thanked: 49 times

Re: Cable tray

Post by gregmcc »

What it comes down to is installing to the conditions, we all know that things like cable tray and switchboards are targets for forklift drivers and it's just a matter of time before they get hit. I have in the past insisted on bollards (which are also a target for the forklift drive) which have proved effective
t92300
Posts: 14
Joined: Mon Apr 13, 2020 8:47 pm
Location: Apprentice
Has thanked: 19 times
Been thanked: 0

Re: Cable tray

Post by t92300 »

DougP wrote:
Wed Nov 11, 2020 8:41 am

That's not going to help the guy on the forklift if he gets off it when the forklift is live though. The cables were only damaged on the forklift side, not the back.
And any electrical worker getting up there to repair, should be isolating it before working on it. With that number of circuits, the only option was isolating the whole building.
The edge of the tray looks damaged by the forklift. The forklift could have been in contact with the tray and live copper at the same time.

The guy on the forklift would have reversed back so that he could inspect the damage wouldn't he? The mast would have been blocking his view of the tray.
AlecK
Posts: 914
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: Cable tray

Post by AlecK »

Earthing the tray would need to be done based on size of largest conductor present.
And even so wouldn't necessarily do any good; as the forklift (or whatever) that caused the damage could be livened without bridging to the tray.

Our rules are designed around dealing with single-fault situations that are "likely"; and as far as this sort of damage goes avoiding is preferable to dealing with the consequences. As Greg said; install for the conditions.
Post Reply