Transportable homes

Post Reply
ElectricalApprentice
Posts: 11
Joined: Mon Apr 13, 2020 8:56 pm
Has thanked: 1 time
Been thanked: 2 times

Transportable homes

Post by ElectricalApprentice »

After reading 3001, am I right in thinking that an a transportable office can be wired using 7 strand 1.5mm tps, with a single circuit feeding all lighting and power points protected by a single 16A RCBO which is also the main switch?
AlecK
Posts: 919
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 355 times

Re: Transportable homes

Post by AlecK »

Yes.
The essential points are
- multi-stranded conductors to cope with flexing / vibration during transport
- current limitation to protect the incoming supply lead & associated fittings
- RCD protection for all final subcircuits.

There's currently no specific requirement for a single means of isolation controlling the entire connectable installation;
and if there were it wouldn't be a "main switch".
More like the (optional) isolating switch on incoming supply to a DB.
These users thanked the author AlecK for the post:
ElectricalApprentice (Thu May 20, 2021 7:31 pm)
Rating: 16.67%