Meter Terminal size

Also includes Works
Post Reply
t92300
Posts: 14
Joined: Mon Apr 13, 2020 8:47 pm
Location: Apprentice
Has thanked: 19 times
Been thanked: 0

Meter Terminal size

Post by t92300 »

Does any one know what the maximum cable size is that can fit in a smart meter terminal?
I'm trying to size the mains cabling for a new house.
PeteRig
Posts: 150
Joined: Sat Apr 25, 2020 2:38 pm
Has thanked: 55 times
Been thanked: 31 times

Re: Meter Terminal size

Post by PeteRig »

I believe its 25mm, if the mains are larger ie long run for volt drop, break the cable down to suit the fusing
These users thanked the author PeteRig for the post:
t92300 (Wed Jun 16, 2021 10:08 pm)
Rating: 16.67%
User avatar
DougP
Posts: 242
Joined: Sun Apr 12, 2020 10:11 pm
Answers: 3
Has thanked: 19 times
Been thanked: 31 times

Re: Meter Terminal size

Post by DougP »

Size the mains to suit the load, distance and installation conditions as usual.
If the cable needs to be smaller for the meter, then just reduce it in the metering enclosure/switchboard.
You would need to check your local network rules or retailer rules to get the exact determination.
I'm pretty sure that the terminals could fit up to 35mm², but that size might not be allowed due to the bend radius limitations.
These users thanked the author DougP for the post:
t92300 (Thu Jun 17, 2021 9:07 pm)
Rating: 16.67%
t92300
Posts: 14
Joined: Mon Apr 13, 2020 8:47 pm
Location: Apprentice
Has thanked: 19 times
Been thanked: 0

Re: Meter Terminal size

Post by t92300 »

Thanks Doug, Pete
DougP wrote:
Thu Jun 17, 2021 7:44 am
Size the mains to suit the load, distance and installation conditions as usual.
If the cable needs to be smaller for the meter, then just reduce it in the metering enclosure/switchboard.
You would need to check your local network rules or retailer rules to get the exact determination.
I'm pretty sure that the terminals could fit up to 35mm², but that size might not be allowed due to the bend radius limitations.
Thanks I was thinking that, I was just trying to see if I could use the cable between the meter board for the tailing down of the mains.

I have since got another person with a bit more experience to look over what I am trying to do.
simmo
Posts: 2
Joined: Fri Aug 06, 2021 8:58 am
Has thanked: 0
Been thanked: 1 time

Re: Meter Terminal size

Post by simmo »

Depending on what make/model of tariff meter it is, its usually and commonly 35mm2 max
These users thanked the author simmo for the post:
t92300 (Wed Aug 11, 2021 7:26 pm)
Rating: 16.67%
Dan L
Posts: 158
Joined: Tue May 19, 2020 10:00 pm
Has thanked: 4 times
Been thanked: 3 times

Re: Meter Terminal size

Post by Dan L »

The EDMI meters are 35mm max

If cables are larger for vd or Ali Must be tailed down to 35mm or less and Cu

Pretty sure that goes for all Cat 1 meters.
These users thanked the author Dan L for the post:
t92300 (Wed Aug 11, 2021 7:27 pm)
Rating: 16.67%
Post Reply