PCE Earth Connection

Post Reply
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

PCE Earth Connection

Post by JamieP »

Screenshot_20200929-132857_Drive.jpg
Is connecting to the earth bar compliant? Or must I physically connect to the main earth?

If the latter, what's the best device to use? Or is terminating into the same tunnel terminal or lug as the main earth sufficient/compliant?
AlecK
Posts: 918
Joined: Thu Apr 16, 2020 11:24 am
Answers: 5
Has thanked: 2 times
Been thanked: 352 times

Re: PCE Earth Connection

Post by AlecK »

"3000" 5.5.2 covers acceptable methods of connecting PECs; Illustrated in Fig 5.3.
It follows that connecting to the earth bar is compliant.
That said; the "should" in "5033" 4.4.2.1 indicates connecting directly to the MEC is preferred.

If you do connect a PEC to the MEC directly, a type of connection that doesn't require cutting / joining the MEC should be used - eg a "line tap"
JamieP
Posts: 478
Joined: Tue Apr 14, 2020 11:08 am
Has thanked: 92 times
Been thanked: 18 times

Re: PCE Earth Connection

Post by JamieP »

Ah, thank you, I had missed that it was a should but regardless good to know